SUA1500 Fan Operation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500 Fan Operation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
6
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

SUA1500 Fan Operation

I just recently purchased a Smart-UPS model SUA1500. I noticed that the fan seems to run continuosly although at a slower speed than the normal high speed that it runs at during battery use or battery charging. Is it supposed to do that? Does anyone else have this model and notice theirs doing the same?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

Ok, so we've established that newer generation models have the fan run constantly at low speed. This seems unneccessary to me, and I think many others would like the option to disable this function.

My biggest concern is that this will drain the battery during an extended power outage. When I turn my unit off, and remove it from power, the fan still continues to run until I disconnect the battery. I would certainly expect the fan to stop running once the unit is turned off.

APC - please hear us on this one!!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

hi.

the fan ISNT supposed to run all the time.

the four things to cause it to run will be:

*•>75% load*
*•on battery*
*•charging the battery*
*•internal temp is higher than 104º*

i am checking to make sure theres nothing else on APC's end that has been changed recently to cause it to remain on because I have seen this before - and also the fact that you said it appears to be different speeds.

please check the above conditions and in the mean time, I will post again if there is a change where it should be running continuously now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

i have confirmed that this was recently changed on the UPS.

so - on newer units, (i dont have a cut off serial number or anything) they do have 2 different fan speeds as you described.

it will be always on, the lower speed when one of those 4 conditions isnt meant and then it speeds up when one of those 4 things happens.

so far, i just know its the SUA1500 - in the process of checking if any other units do this as well.

do you mind posting the first digits of your serial number? You can just post the QSXXYY portion of it if you'd like.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:32 AM . Last Modified: ‎2024-03-08 02:26 AM

Thank you for your reply. The first few digits of the serial number are AS0745.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

ok, thank you. that is from the 45th week of 2007.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

So when you said newer UPS, what is the manufacturer date to be considered newer?
Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:26 AM

Ok, so we've established that newer generation models have the fan run constantly at low speed. This seems unneccessary to me, and I think many others would like the option to disable this function.

My biggest concern is that this will drain the battery during an extended power outage. When I turn my unit off, and remove it from power, the fan still continues to run until I disconnect the battery. I would certainly expect the fan to stop running once the unit is turned off.

APC - please hear us on this one!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore