SUA1500 Buzzing Noise Late at Night

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500 Buzzing Noise Late at Night
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
5
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

SUA1500 Buzzing Noise Late at Night

I have been running a APC smart UPS SUA 1500 for just about 30 days now and have noticed in the last week that it emits a transformer-like buzzing noise every night starting at about 10:30 or 11:00 pm.; by morning the buzzing has stopped. No buzzing during the day - only at night starting at around 10:30. The UPS is running at 30% load (high sensitivity), the largest draw being a 2009 quad core MAC Pro desktop and NEC LCD monitor.

From the data log the voltage drops in the evening to about 113v while during the day it is usually at 118v but will vary between 118v and 115v until late evening when it drops to 113v and stays there. Apparently the 113v level is not low enough to trigger battery or boost operation but does seem to cause the buzzing. My question is, is this normal/expected behavior for the UPS given the line condition at my location or is this particular UPS unit defective? I have a APC 1000 XS plugged into the same outlet as the SUA1500 and it does not buzz.

Stan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:56 AM

I have been running a APC smart UPS SUA 1500 for just about 30 days now and have noticed in the last week that it emits a transformer-like buzzing noise every night starting at about 10:30 or 11:00 pm.; by morning the buzzing has stopped. No buzzing during the day - only at night starting at around 10:30. The UPS is running at 30% load (high sensitivity), the largest draw being a 2009 quad core MAC Pro desktop and NEC LCD monitor.

From the data log the voltage drops in the evening to about 113v while during the day it is usually at 118v but will vary between 118v and 115v until late evening when it drops to 113v and stays there. Apparently the 113v level is not low enough to trigger battery or boost operation but does seem to cause the buzzing. My question is, is this normal/expected behavior for the UPS given the line condition at my location or is this particular UPS unit defective? I have a APC 1000 XS plugged into the same outlet as the SUA1500 and it does not buzz.

Stan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

Techie wrote:
Hi Stan,

I would like to gather some more information from you before making any comments about this issue..Has it been happening since you installed the UPS? What lights are on the front of the UPS when it is buzzing? If possible, stimulate a power failure by unplugging the UPS from the wall and see if the UPS emits the same kind of noise which is similar to the noise that you are referring to.
I have had the UPS for approx. 30 days. I only noticed the buzzing in the last week late at night. No unusual front panel lights come on during the buzzing - the load (one segment) light , on-line light and battery charge light are the only lamps lit during the buzzing. By the way, last night there was no buzzing even though the in coming voltage was consistently at about 109-110v most of the late evening (it did go as low as 108 and the boost light lit for awhile but no buzzing). I pulled the plug for about 30 seconds and no unusual noise - no buzzing - just the fan revving up a bit in response to battery power mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

Are you sure that the other equipment is not the source of the buzzing? I have seen in many cases that the other equipment which is plugged to the UPS caused the buzzing noise. Is the buzzing noise abnormally loud?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

Techie wrote:
Are you sure that the other equipment is not the source of the buzzing? I have seen in many cases that the other equipment which is plugged to the UPS caused the buzzing noise. Is the buzzing noise abnormally loud?
When the buzzing occurred it was definitely coming from the UPS. How do I know? I turned off all devices except the ups. The buzz was loud enough for me to want to walk away from the workstation. At any rate I did not have the buzzing last night and do not have it now, so it is intermittent and apparently not caused by the variations in incoming line voltage. Still puzzled.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:15 AM . Last Modified: ‎2024-03-14 12:56 AM

At this time, I recommend you to monitor the UPS performance for another couple of days and see if the same kind of buzzing comes from the UPS.

secondly, It is normal for the unit to emit noise when the fan inside the unit is operating. this [k-base|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6672] has got the reasons the fan in my Smart-UPS will come on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:56 AM

0 Likes
0
1572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:16 AM . Last Modified: ‎2024-03-14 12:56 AM

I have been running a APC smart UPS SUA 1500 for just about 30 days now and have noticed in the last week that it emits a transformer-like buzzing noise every night starting at about 10:30 or 11:00 pm.; by morning the buzzing has stopped. No buzzing during the day - only at night starting at around 10:30. The UPS is running at 30% load (high sensitivity), the largest draw being a 2009 quad core MAC Pro desktop and NEC LCD monitor.

From the data log the voltage drops in the evening to about 113v while during the day it is usually at 118v but will vary between 118v and 115v until late evening when it drops to 113v and stays there. Apparently the 113v level is not low enough to trigger battery or boost operation but does seem to cause the buzzing. My question is, is this normal/expected behavior for the UPS given the line condition at my location or is this particular UPS unit defective? I have a APC 1000 XS plugged into the same outlet as the SUA1500 and it does not buzz.

Stan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore