are the batteries on a SUA1000RM2U hot swap?
i would like to avoid having to shutdown the UPS if possible.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:19 AM . Last Modified: 2024-03-11 02:41 AM
yes, any SUA UPS batteries are hot swappable. the UPS will of course tell you temporarily that the battery is disconnected by flashing the replace battery LED and during this time you have no batteries connected, you'll have no battery back up if there is an outage or blip in those few minutes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:19 AM . Last Modified: 2024-03-11 02:41 AM
yes, any SUA UPS batteries are hot swappable. the UPS will of course tell you temporarily that the battery is disconnected by flashing the replace battery LED and during this time you have no batteries connected, you'll have no battery back up if there is an outage or blip in those few minutes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:19 AM . Last Modified: 2024-03-11 02:41 AM
ok thanks.