SUA1000RM2U and PowerChute logs innacurate

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1000RM2U and PowerChute logs innacurate
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
7
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

SUA1000RM2U and PowerChute logs innacurate

Whenever I come in to work and discover there was a power failure, I check PowerChute's log. It always states the time the power failed and the time it went to low battery state as the same time. I can never tell exactly what happened. The UPS is under 45% load and was recently tested to hold power for about 28 minutes.

It would be nice if I knew

When the power went down.
When the battery went to low state.
When PowerChute decided to shut down.

Any ideas?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

hi again,

yeah you are right - the pings dont explain the low battery warning coming up so fast so thats why I am skeptical on that.

look forward to seeing the results!

glad to be of help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

hi,

can you check what your low battery signaling time is set to in powerchute? also, about how old is the UPS? if you can provide the first digits of the serial number - such as XX0625 that can tell us the age.

to find the low battery signaling time via the business edition console, right click on the device and go to device properties. on the left hand side, expand the shutdown section and then choose power failure. please let us know the settings you have chosen in here.

if you access the agent via the web interface, click on protected system on the left hand side, and then let us know what you see on that first screen. mainly i need the "Low Battery Signal" but everything on that screen would be nice. to access this screen - you can go to http://127.0.0.1:3052 on the machine connected to the UPS or go to http://:3052 if you are remote. this may be easier.

if you can access it via the web browser interface, see if you can copy and paste a little bit of the event and data logs so we can take a look at those.

also, how much runtime does the UPS actually report? i see that you say it lasted 28 minutes but is that what the software says as well?

hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

Thanks for the reply. The test I did was from simply pulling power cord and monitoring the led level. I did not let it get too low so it could have gone longer than 28 minutes.

Serial # AS0632330255
Manufacture date 8/1/06
Firmware is 618.3D

Runtime says 33min
Power Fail procedure is as follows:

Begin Shutdown After UPS has been on battery for 15 minutes
When Power returns, reboot UPS immediately.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

Time Required For Shutdown Sequence 5 Minutes
Low Battery Signal 120 Seconds
Command File Enabled No
OS Shutdown Delay 3 Minutes
OS Shutdown Type Shutdown
Enable OS Reboot Yes
UPS Turn On Battery Capacity 0 %
UPS Turn On Delay 0 Minutes
Enable SMTP E-mail No
Enable Notification No
Enable Logging Yes

Message was edited by: fizzak

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

The log...Two things I dont get, one is time between power failed and low batt and two, it appears the power failed for only a few seconds...

8/20/08 09:37:42 Sufficient Runtime Available
8/20/08 09:35:18 Insufficient Runtime Available
8/20/08 09:35:03 Sufficient Runtime Available
8/20/08 09:34:54 Insufficient Runtime Available
8/20/08 09:34:08 Sufficient Runtime Available
8/20/08 09:33:35 Insufficient Runtime Available
8/20/08 09:33:35 Communication Established
8/20/08 09:33:35 Monitoring Started
8/20/08 09:09:59 Monitoring Stopped
8/20/08 09:09:52 Insufficient Runtime Available
8/20/08 09:09:52 Power Restored
8/20/08 09:09:49 Shutdown process started
8/20/08 09:09:49 Insufficient runtime has been detected, PowerChute Business Edition will now start an immediate shutdown.
8/20/08 09:09:49 Low Runtime Remaining
8/20/08 09:09:49 Low Battery
8/20/08 09:09:49 Power Failed
8/20/08 09:09:42 Insufficient Runtime Available
8/8/08 15:09:21 Communication Established
8/8/08 15:09:21 Monitoring Started
8/6/08 09:12:06 Self Test Passed
8/6/08 09:12:00 Self Test Initiated
8/1/08 12:08:57 Communication Established
8/1/08 12:08:57 Monitoring Started
8/1/08 12:05:24 Monitoring Stopped
8/1/08 10:50:14 Communication Established
8/1/08 10:50:14 Monitoring Started
8/1/08 10:49:35 Monitoring Stopped
7/29/08 23:41:51 Communication Established
7/29/08 23:41:51 Monitoring Started
7/29/08 23:39:57 Monitoring Stopped
7/23/08 09:12:29 Self Test Passed
7/23/08 09:12:26 Self Test Initiated
7/23/08 07:18:43 Communication Established
7/23/08 07:18:43 Monitoring Started
7/23/08 07:16:22 Monitoring Stopped

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:37 AM

hi,

you are right. this doesnt really make sense. these "Power failed" events dont look legitimate to me. based on your shutdown configuration, which looks fine, it shouldnt shut anything down immediately or even attempt to.

has this UPS always done this?

i was going to suggest braindeading the UPS to reset the communication inside of it.

to do that:

you'd need to power down your UPS load and then unplug it. turn off the UPS and remove any communication cables - so USB or serial. unplug the UPS from the wall. then hold down the off (o) button until you hear a click and see the LEDs flash. hold it down for at least 10 seconds if you dont hear anything. then plug it back in, and reconnect everything and lets go from there.

at least we can get a fresh start and see if it needs a simple reset.

i just remembered - i have seen a bunch of "Power failed" events when the power/electrical company "pings" their meter at your location for information and the UPS interprets them as power outages because it causes a problem with the waveform on the line. do you know of anything like this? it doesnt explain the low battery events right after but who knows if thats related to the "power failed" events. just throwing it out there! let's braindead first if you can.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

Yea, it did this once before. Thats why I decided to try the unplug test. I'll try cycling the power like you suggested. Will be a few days before I can post a result.

The ping is entirely possible like you said but doesn't explain the transition to low batt and shutown within 4 seconds. Perhaps its freaking out the UPS?, perhaps I dont have it grounded well enough? I don't know.

Appreciate your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:32 PM . Last Modified: ‎2024-03-15 01:36 AM

hi again,

yeah you are right - the pings dont explain the low battery warning coming up so fast so thats why I am skeptical on that.

look forward to seeing the results!

glad to be of help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore