SUA 1000XL Heating Up

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA 1000XL Heating Up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

0 Likes
3
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

SUA 1000XL Heating Up

I have a SUA 1000XL and one SUA24XLBP, both purchased from APC in 2003.

Load is very light with only one or two occurances of total discharge.

Lately the fan on the 1000xl comes on for 10min every 30min. The sides of the case are very warm.
(The 24xlbp is cool to the touch.)

The 1000xl self tests ok, there are no indicator lamps stating the battery(s) need to be replaced.

No powerchute sw monitoring at the moment...

How can I be sure the problem isn't the hardware before spending money for fresh batteries?

(APC chat and phone support was not conclusive)

Thank you,
Flav

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:32 PM . Last Modified: β€Ž2024-03-15 01:37 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:32 PM . Last Modified: β€Ž2024-03-15 01:37 AM

yes i agree. worst case, if you buy the batteries through APC, you can return them within 30 days of purchase but may be subject to a restocking fee πŸ˜•

keep us updated if you can!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

are you able to take the batteries out and look at them to see if they are a bit swollen or anything?

the four reasons the fan may come on are:

1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 140 degrees F (60 degrees C). Note, for 4G units (model number begins with SUA, the temperature range has changed. For these models, the internal temperature will have to be greater than 104 degrees F (40 degrees C)

at least if you install powerchute on a computer and hook it up, we can see what the internal temperature is but i'd take a look at the batteries themselves first to see if there is anything obviously wrong with them.

the batteries are ~6 years old so a proactive replacement wouldnt be a bad idea if we make sure the UPS isnt at fault first.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:31 PM . Last Modified: β€Ž2024-03-15 01:37 AM

Thanks for your reply.

I know I need to physically check the batteries for any signs of stress. Hopefully it'll be obvious e.g. swollen, thus reducing the risk of investing in new batteries (but then still having a problem with the HW).

Flav

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:32 PM . Last Modified: β€Ž2024-03-15 01:37 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:32 PM . Last Modified: β€Ž2024-03-15 01:37 AM

yes i agree. worst case, if you buy the batteries through APC, you can return them within 30 days of purchase but may be subject to a restocking fee πŸ˜•

keep us updated if you can!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore