SUA 1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
6
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:00 AM . Last Modified: ‎2024-03-13 11:34 PM

SUA 1500

The model number is actually SUA1500

I saved a SMT 1500 from the trash yesterday. I got it home and plugged it in, and when I powered it on, the online light blinked a few times, then the alarm went off and the replace battery light was flashing. This thing looked as though it had never been used, so I popped it open to see if there were any smoking guns inside. Inside was imaculate, and I took a voltage reading and got 26VDC. I put it back together, simply plugged it in and I had 1 charge light lit. Let it sit for a half hour and a second lit. I thought great, the battery was completely discharged and just needed to get charged up. Left it plugged in a few hours and went up to 5 bars. I was happy and left it plugged in over night. This morning I hit the power/test button and I got the dang alarmn and replace battery light again. I opened the disconnect on the back and took some voltage readings there, and I was getting 17.5VDC. I got confused and opened it up again and took a reading at the terminals and got 27VDC. So this thing did a proper charge, but there is something else wrong internally it looks like. I am trying to figure out how to repair this thing, but I'm not sure how to move ahead without schematics or drawings. I am pretty sure the battery itself is good, as 27vdc sounds about right for a 24v lead acid battery. But 17.5vdc at the disconnect doesnt sound right at all. And Im guessing the circutry is sensing this bad voltage and that is why I am getting the replace voltage warning.

Any ideas out there?

Message was edited by: blitzgp

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

You need to replace the batteries and it will probably be fine.

Old lead acid batteries that are almost totally shot can sometimes be recharged a very small amount, totalling something like 0.1% of the original capacity.

Most battery chargers are stupid and only measure cell voltage to determine charge status, but cannot tell what actual capacity is available. So yeah as you charge the ruined battery, cell voltage does slowly climb, so yeah the charge indicator also climbs.

But full charge in this case means practically nothing since what you have is maybe 0.1 amp-hours available in a "fully-charged" battery pack that was supposed to hold 100 amp-hours. Put any actual load on it like the UPS self-test, and battery voltage instantly bottoms out because it cannot supply the amperage to maintain the voltage.

The charge indicator on the UPS is mostly a liar, which is why run-time calibrations are needed to make the UPS more honest about what amount of runtime really is still available in an old battery pack.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

The model number is actually SUA1500

I saved a SMT 1500 from the trash yesterday. I got it home and plugged it in, and when I powered it on, the online light blinked a few times, then the alarm went off and the replace battery light was flashing. This thing looked as though it had never been used, so I popped it open to see if there were any smoking guns inside. Inside was imaculate, and I took a voltage reading and got 26VDC. I put it back together, simply plugged it in and I had 1 charge light lit. Let it sit for a half hour and a second lit. I thought great, the battery was completely discharged and just needed to get charged up. Left it plugged in a few hours and went up to 5 bars. I was happy and left it plugged in over night. This morning I hit the power/test button and I got the dang alarmn and replace battery light again. I opened the disconnect on the back and took some voltage readings there, and I was getting 17.5VDC. I got confused and opened it up again and took a reading at the terminals and got 27VDC. So this thing did a proper charge, but there is something else wrong internally it looks like. I am trying to figure out how to repair this thing, but I'm not sure how to move ahead without schematics or drawings. I am pretty sure the battery itself is good, as 27vdc sounds about right for a 24v lead acid battery. But 17.5vdc at the disconnect doesnt sound right at all. And Im guessing the circutry is sensing this bad voltage and that is why I am getting the replace voltage warning.

Any ideas out there?

Message was edited by: blitzgp

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

I am having a similar experience with two SUA1000's. I installed new batteries in both and get similar results. Proper voltages, minimal heat, full charge as indicated by both status lights and powerchute. But when I reset the units the charge goes back to nothing, the batteries still show 27.4 volts but the unit starts another charge cycle. I thought I might have picked up bad batteries until I tried a battery from a fully functioning SUA1500 in both units and got the same results. I expect it's something wrong with the charging circuit, possibly the mosfet's but I haven't had time to check them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

whem i pulled the battery i pulled off the plastic cover on the vents/terminals and tested there. after it went throught he charge cycle, i tested at the disconnect and got the 17.5, which made no sense, so i pulled the battery again and tested and got 27. i might not have been using the correct terminals, but i did test the battery directly and saw a 1v increase from pre charge and post charge. however, when i retested the unit and got the alarms, i was doing some of the other tests, like just using battery power and i was having all sorts of light shows and beeps. i was testing using a tiny fan as the load, and it would sporadically power up and down as i was testing. After my tests, i plugged the unit back in and it started the charging sequence over again. Started off with online light lit, and the bottom charge light blinking, then after a while went solid, and at this point, the 4th light is lit. Is this charge circuitry voltage based or time based? I am waiting for it to finish this charge cycle, but it is not generating any heat, so I dont think it is doing anything at all.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

when i plug it in, there is either 1 solid light or 1 blinking light in the battery bar which should be 0-24% battery capacity per the instruction manual. its probably just based off voltage, which in reality should be 20VDC (I dont know the exact curve for the specific battery, but with a 24VDC nominal voltage and a 27-28vdc max capacity voltage, 20vdc sounds about right for a fully discharged battery). Over a period of a 1-2 hours, the lights will slowly light up until all 5 are lit. This will stay like this indefinately, the online light lit and 5 battery capacity lights lit. When I unplug the unit, the battery capacity light drops to 1 or 2 bars, does the normal alarm that you are on battery power, then after a few min, the continuous alarm goes off indicating 2 min left, but this only lasts for 15-20 seconds. However, the battery still has 27vdc taken at the internal disconnect. I am trying to decide if there is a problem with the battery or the circuitry.

edit the test load I was using is a tiny little fan that draws hardly any current. I also added a 100w light, but it would only power on for a very short amount of time.

I got it for the price of "not putting it in the garbage", and I assume it is out of warranty so there is no point to pay for it to be serviced or looked at, on top of shipping a 50lb unit around. However, if it is just a burned out battery, the cost of a replacment is actually justifiable for a commercial grade ups.

I am kind of leaning towards a circuitry issue, because no heat is generated in the cell. If there was any internal short, this sucker would heat up pretty bad. It should also heat up on charge or discharge, which it is not. So basically I am getting conflicting indications. On the charge cycle (which is why I was asking if the charge cycle was time based because larger battery charges are in fact time based) I get the lights indicating a full charge (along with on contact voltage readings), but during discharge mode, it indicates 24% or less, and rapidly decays to 0 in under a minute.

Basically my next step is to turn this into a science experiment and gut the unit and attempt to weld with the battery to test its actual capacity, but I dont want it to come down to that, lol.

Message was edited by: blitzgp

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

does the powerchute software allow you to perform equilizing charges? or any other special charges and or capacity testing? i havent been able to install it yet because i cant find any of the old scholl stadard usb cables

Reply

Link copied. Please paste this link to share this article on your social media post.

Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

0 Likes
0
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:01 AM . Last Modified: ‎2024-03-13 11:34 PM

You need to replace the batteries and it will probably be fine.

Old lead acid batteries that are almost totally shot can sometimes be recharged a very small amount, totalling something like 0.1% of the original capacity.

Most battery chargers are stupid and only measure cell voltage to determine charge status, but cannot tell what actual capacity is available. So yeah as you charge the ruined battery, cell voltage does slowly climb, so yeah the charge indicator also climbs.

But full charge in this case means practically nothing since what you have is maybe 0.1 amp-hours available in a "fully-charged" battery pack that was supposed to hold 100 amp-hours. Put any actual load on it like the UPS self-test, and battery voltage instantly bottoms out because it cannot supply the amperage to maintain the voltage.

The charge indicator on the UPS is mostly a liar, which is why run-time calibrations are needed to make the UPS more honest about what amount of runtime really is still available in an old battery pack.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore