SUA 1000i disconnected battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA 1000i disconnected battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
6
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

SUA 1000i disconnected battery?

Hi ,

the red light is blinking every about two seconds.
The battery is connected and the protection on the back is secure!
If I disconnenct it from the power outlet the UPS is shutting down.

Could you please help me?

Thank you


EDIT

some times I manage to get rid of the red light but it blinks again after a while.

Message was edited by: Yiannis

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

Hi ,

the red light is blinking every about two seconds.
The battery is connected and the protection on the back is secure!
If I disconnenct it from the power outlet the UPS is shutting down.

Could you please help me?

Thank you


EDIT

some times I manage to get rid of the red light but it blinks again after a while.

Message was edited by: Yiannis

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:43 PM

The LED that is flashing on your UPS is the replace battery LED, is this correct?

Yes .

Are there any other LED/ indicator that is lit up?

Yes the online LED.

If you are seeing a flashing replace battery LED, it means that the unit fails to detect the battery and this is accompanied by some chirping sound coming from the UPS.

Yes there is a beep.Sometimes it stops and it starts again in random time.

Do you have a spare UPS of the same model? We can swap the batteries to see if the issue clears.

No I haven't .

Message was edited by: Yiannis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:50 AM . Last Modified: ‎2024-03-13 11:42 PM

Have you tried unplugging the UPS while it is online? If you did, what happened to the unit and the load? There are cases wherein by just replacing the battery the issue clears but for some it ends up on UPS replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

Yes I have.

It just shutdown.

I will replace the battery tomorrow and see what will happen

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

I have replaced the battery and everything is back to normal!!!!!

I have replaced ONLY one battery because the other one seems to be ok,for the moment.
It has enought "Ah" for now.

Is there any problem by replacing only one battery?Is it possible the old one to damage the new?

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

We always recommend replacing all/ both batteries since if you have an old/ bad battery and you've combined it with a new one, it will affect the new one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:51 AM . Last Modified: ‎2024-03-13 11:42 PM

Hi ,

the red light is blinking every about two seconds.
The battery is connected and the protection on the back is secure!
If I disconnenct it from the power outlet the UPS is shutting down.

Could you please help me?

Thank you


EDIT

some times I manage to get rid of the red light but it blinks again after a while.

Message was edited by: Yiannis

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore