Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SU700RMNET won't calibrate with calibration key,E

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU700RMNET won't calibrate with calibration key,E
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

0 Likes
1
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

SU700RMNET won't calibrate with calibration key,E

Will the calibration key not work on the SU700RMNET? Serial # WS9646118180.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

0 Likes
0
881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

I believe it should work. Make sure you just replaced the battery then follow the below instructions. One common thing to check for is any smart-slot accessory like an interface expander (two serial ports) or a network management card in the UPS. Make sure you remove any smart-slot accessory.

1. Verify the UPS is a 3rd generation Smart-UPS (see other side for model name description).

2. Stop any connected Powerchute software from running and disconnect any serial cable from the UPS.

3. Remove any Smart-slot accessory. If there is no accessory, proceed to step 4. In order to remove an accessory from the Smart-slot:
a) First power down any load connected to the UPS, then power off the UPS by pressing the front panel off (o) button.
b) Unplug the UPS from the wall.
c) Next, push and hold the front panel off button for approximately 4 seconds (listen for a faint clicking sound in the UPS).
d) Now remove the accessory from the Smart-slot.
e) Plug the UPS back into a live utility outlet.

4. Make sure UPS is on, if not push the front panel on (I/Test) button and wait for the completion of the auto self-test routine.

5. Connect the calibration key to the UPS communication port (DB9 connector on UPS rear panel).

6. Monitor the LEDs on the front of the UPS. If, after a few seconds, all LEDs flash and the UPS beeps, the recalibration was a success.

7. If the red LED of the calibration key lights, there was a failure. In case of failure, re-verify that steps 1 through 5 above were followed correctly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:03 AM . Last Modified: ‎2024-03-08 01:39 AM

I believe it should work. Make sure you just replaced the battery then follow the below instructions. One common thing to check for is any smart-slot accessory like an interface expander (two serial ports) or a network management card in the UPS. Make sure you remove any smart-slot accessory.

1. Verify the UPS is a 3rd generation Smart-UPS (see other side for model name description).

2. Stop any connected Powerchute software from running and disconnect any serial cable from the UPS.

3. Remove any Smart-slot accessory. If there is no accessory, proceed to step 4. In order to remove an accessory from the Smart-slot:
a) First power down any load connected to the UPS, then power off the UPS by pressing the front panel off (o) button.
b) Unplug the UPS from the wall.
c) Next, push and hold the front panel off button for approximately 4 seconds (listen for a faint clicking sound in the UPS).
d) Now remove the accessory from the Smart-slot.
e) Plug the UPS back into a live utility outlet.

4. Make sure UPS is on, if not push the front panel on (I/Test) button and wait for the completion of the auto self-test routine.

5. Connect the calibration key to the UPS communication port (DB9 connector on UPS rear panel).

6. Monitor the LEDs on the front of the UPS. If, after a few seconds, all LEDs flash and the UPS beeps, the recalibration was a success.

7. If the red LED of the calibration key lights, there was a failure. In case of failure, re-verify that steps 1 through 5 above were followed correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore