SU3000RMXL3U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU3000RMXL3U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
3
1315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

SU3000RMXL3U

I was cleaning/testing a used SU3000 that I had purchased in unknown condition.  The battery tray was connected with a slight arc (seems typical).  However, when I applied 120 volt AC, there was a definitive "spark" that seemed to originate around the front of the H bridge heat sinks.  I could not see any visible damage, so I continued testing.  The unit started up, ran a 20% and 70% load on batteries  without any problems.  The batteries are charging.  No "events" were logged, and self test passed.

The unit was not extremely dusty/dirty and was gently cleaned with compressed air before any testing was done.  I was certainly surprised that the unit seems to function fully after any arcing around the motherboard.  Any explanation for this "spark" that seemingly did not damage the unit?  I have an oscilloscope - should I check the output wave form?

Any suggestions are appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

Joe;

Yes there are a total of 32 of the mosfets - 8 on each section of the "H".  Fully populated heat sinks.  I'm going to check on some "spare parts units" to see if I can find a similar rated transistor and do a "repair".  Not much to lose on this one.  Everything else looks - so why not!

Thanks, Mark

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:33 AM . Last Modified: ‎2024-03-18 04:33 AM

After closer inspection, it is apparent that mosfet Q78 failed as the case is split.  All four heat sinks are fully populated on this unit.  Is it possible to continue using this unit - maybe at a reduced back up load?  Or is it likely that this is the beginning of a chain reaction failure.  The unit was manufactured in 2007.

If I replace this one mosfet, can I expect to have reasonable service out of the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

Mark, as I am sure you're aware, Schneider/APC doesn't recommend, condone or otherwise support repair of these units.

I find it amazing that the unit continues to work in spite of the fact that one of the transistors failed (failed open, obviously).  Also speaks to the excellent design of the unit.  Several of those "Q's" must be in parallel to support increased current capabilities and loosing one or more would put added stress on those that remain.  That being said, sure, why not get another one and try and keep the unit working?  You, of all people, should have no problem getting in there and messing around.

Good luck! 

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:34 AM . Last Modified: ‎2024-03-18 04:33 AM

Joe;

Yes there are a total of 32 of the mosfets - 8 on each section of the "H".  Fully populated heat sinks.  I'm going to check on some "spare parts units" to see if I can find a similar rated transistor and do a "repair".  Not much to lose on this one.  Everything else looks - so why not!

Thanks, Mark

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore