SU1400RM2U Beeps Continuously - Replace LED Flashing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU1400RM2U Beeps Continuously - Replace LED Flashing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

0 Likes
2
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

SU1400RM2U Beeps Continuously - Replace LED Flashing

SU1400RM2U beeps every 3 secs when plugged in and replace battery LED flashes amber. I read the repair manual and it states:

?Replace battery light flashes, battery charge bar graph is off, and the UPS beeps continuously.
• Battery not connected properly. Check that the battery connector is fully engaged.

I reconnected the battery several times, but no change. Do the batteries need to be replaced or is this a different problem?

Thanks
Lance

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

0 Likes
0
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

how old are the batteries in the UPS?

this indicator basically means that the UPS is unable to detect the batteries being connected to it. this can be caused by what you already checked, which are the phyiscal battery connections, or by the voltage in the batteries being too low where the UPS cannot see any voltage present.

i'd recommend checking the voltage on the batteries if you can. if they are new batteries (an APC RBC), we may need to proceed further in determining if there is a internal fault with the UPS causing it to report that it doesnt see the batteries anymore.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

0 Likes
0
555
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

Thanks for the response, not sure the exact age on the batteries...probably 3 years. I'll check the voltage and report back.

Thanks and Merry Christmas!

Message was edited by: merkleyla

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

0 Likes
0
556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:08 PM . Last Modified: ‎2024-03-15 01:28 AM

how old are the batteries in the UPS?

this indicator basically means that the UPS is unable to detect the batteries being connected to it. this can be caused by what you already checked, which are the phyiscal battery connections, or by the voltage in the batteries being too low where the UPS cannot see any voltage present.

i'd recommend checking the voltage on the batteries if you can. if they are new batteries (an APC RBC), we may need to proceed further in determining if there is a internal fault with the UPS causing it to report that it doesnt see the batteries anymore.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of