Matrix 3000 battery communication cable-HELP!!!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 3000 battery communication cable-HELP!!!!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
11
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

Matrix 3000 battery communication cable-HELP!!!!

We moved our office and somehow the battery communication cable got lost. We have the Matrix Smartcell XL battery module.

This apparently isn't a regular RJ-11 jack and without it the UPS constantly displays "no battery communication". I've scoured this site and eBay for replacement but so far no luck. Could someone more knowledgeable than myself tell me where I could get one of these or what the part number is so I can order it. Maybe even what kind of jack this is.

Merry Christmas!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • smartups_1400
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

He bought second-hand Matrix 5000 and I do not have the connection cable, could you tell me how to make one?
Can you send me by mail?
regards

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

i cant give you the details on the cable since its marked as proprietary but please confirm your email address in your profile and I can submit an order and hopefully get you a cable for monday if you tell me by about 2pm EST.

i would hope that would be agreeable πŸ™‚

also - be prepared to provide your shipping address/contact phone # when I email you πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

hi

this is a 4 wire crossover RJ-9 cable i believe - APC part # 0W0271-A

i can check stock on this for you tomorrow and check how we can get you one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

Thank you so much. I've sent an email to tech support as well. I'm looking forward to getting this thing back online.

Again I really appreciate your help in this matter. This is why I always buy APC. Best product, even better people.

_____________

I can get RJ-9 connectors here local. I'll assume when you say "crossover" you mean the wires flip 180 degrees when crimped or do they flip on each side?

Either way i'm in a pickle and need one ASAP. My boss is going to freak when he finds out. I don't really like my job but I don't want to lose it either. He's just itching to can me and I don't need to add to his ever growing list of reason to let me go.

Thank you!

Message was edited by: chopfooey

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

Thanks for the super quick reply. According to tech support this cable is a standard phone headset cable and I can get one from Radio Shack or Wally World.

I really appreciate your help. Your service is the standard by which I judge others and many fall far short. I only wish every company was as concerned about their customers as you.

Best wishes to you and yours this holiday season.

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

i am pretty sure its not standard...it is the same RJ-9 connector though.

let me know if you still need it afterwards.

happy holidays to you too πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

According to the email from Tech support it's a standard phone headset cable. The curly one from the base to the headset. I hope so because the email also said they don't sell the cord separately it only comes with a new XL pack.

I will try the RJ-9 headset cable later today and get back with you.

Again thank you so much for your time and consideration in this matter.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

i removed your address/contact info from the post but saved it myself so you dont get spammed, etc

let me know how you make out. after investigating, i guess it will work. someone tried it out supposedly here.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

oh and FYI - the UPS will still function correctly and go to battery and all that stuff - the only things it CAN'T do/tell you without the battery comm cable are - the number of batteries you have, their type (smartcell/smartcell-XR), and their status/health (good/bad). it will still go to battery during a power problem just as it normally would.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

The new cable I purchased didn't work but one I found on an old rotary phone worked fine. Go figure.

The UPS is now happy and so am I.

Thanks for all your help in this matter.

Rarely do I get to deal with a company of such caliber.

Message was edited by: chopfooey

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

glad it worked out πŸ˜‰

i appreciate the comments as well. please let us know if you need anything else!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

0 Likes
0
1450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:08 PM . Last Modified: β€Ž2024-03-15 01:28 AM

He bought second-hand Matrix 5000 and I do not have the connection cable, could you tell me how to make one?
Can you send me by mail?
regards
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore