SSL/TLS Email: Test e-mail failed; SMTP configuration error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SSL/TLS Email: Test e-mail failed; SMTP configuration error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
SheldonDsouza
Crewman SheldonDsouza
Crewman

Posted: ‎2022-08-29 04:32 AM . Last Modified: ‎2022-08-29 04:46 AM

0 Likes
6
4434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 04:32 AM . Last Modified: ‎2022-08-29 04:46 AM

SSL/TLS Email: Test e-mail failed; SMTP configuration error

We are trying to configure 2 types of APC UPS in our environment:

 

Smart-UPS RT 6000 RM XL

 

Model Number:AP9631
Serial Number:5A1142T00064
Hardware Revision:05
Name:aos
Version:v5.1.3

 

SMTP Server is set with Authentication (Username and Password), but there is no advanced option for TLS

 

Smart-UPS 3000

 

Model Number:Smart-UPS 3000
Serial Number:AS2037164231
SKU:SMT3000RMI2UC
Firmware Revision:UPS 03.7 (ID1015)
Name:aos
Version:v6.5.6

 

SMTP Server is set with Authentication (Username and Password), and we have tested out SSL/TLS (Port 587) (Always, If Supported and Implicitly) but all three gives the error 
 
Test e-mail failed; SMTP configuration error.
 
Last Server Response
220 2.0.0 Ready to start TLS
 
There is no CA Root Certificate Set. Also both the UPS Firmware are not updated. 
 
Could someone assist on how to solve the issue. (We have checked and tested out the credentials and they are working fine on other devices that require SMTP TLS.)
 
Also if Firmware needs to be updated, could someone guide on the exact firmware that needs to be downloaded for these models.
 
Both UPS are having: UPS Network Management Card 2.
 

Note: If we use SMTP Port 25 Authentication (Username and Password) with not TLS , it works perfectly and we receive the Test Mail. But we require to use SSL/TLS in our environment.

 
Thanks!
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-29 07:35 AM

0 Likes
4
4421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 07:35 AM

@SheldonDsouza 

 

The cards are running very old firmware. You should update to the latest.

Here is a link: 

https://www.apc.com/us/en/product/SFSUMX708/ups-network-management-card-v7-0-8-firmware-for-smartups...

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SheldonDsouza
Crewman SheldonDsouza
Crewman

Posted: ‎2022-08-30 01:23 AM

In response to BillP
0 Likes
3
4404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 01:23 AM

@BillP I have managed to update the Firmware for the UPS and they are now showing the latest version v7.0.8

However, when we perform the SMTP Test, it's the same issue. (Do we need to reboot the UPS?)

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-08-30 07:47 AM

In response to SheldonDsouza
0 Likes
2
4394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 07:47 AM

@SheldonDsouza 

 

You do not need to reboot. The NMC reboots when the firmware is updated.

 

What SMTP service are you using? Google, Outlook, etc.? I know that with Gmail there is a requirement for two-part authentication. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SheldonDsouza
Crewman SheldonDsouza
Crewman

Posted: ‎2022-08-30 11:01 AM

In response to BillP
0 Likes
1
4390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 11:01 AM

@BillP, its a custom SMTP Server (Exchange Server Relay) smtpmail.shj.ae

 

Initially, the Organization provided us with an Open Relay that worked with Port 25 (Authentication with Username and Password but not TLS), till they changed it to a secure relay with Port 587

 

As said earlier those credentials work perfectly on other Devices where we changed to TLS, but for some reason, it doesn't work with the APC UPS. I can't find a way to Telnet from the UPS device as no commands are present. DNS Server set on the UPS device is resolving the IP of the Exchange Relay (DNS Test)

 

Is there a log that I can get that shows what seems to be happening (Detailed Log)

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SheldonDsouza
Crewman SheldonDsouza
Crewman

Posted: ‎2022-09-01 01:14 AM . Last Modified: ‎2022-09-01 07:02 AM

In response to SheldonDsouza
0 Likes
0
4354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-01 01:14 AM . Last Modified: ‎2022-09-01 07:02 AM

@BillP You have any update on what needs to be done?

I have also updated the Device Firmware to SMT1015UPS_04-6

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JohnB58
JohnB58
Cadet

Posted: ‎2023-01-22 08:27 PM

0 Likes
0
3982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-22 08:27 PM

@BillP I stumbled upon this as I was researching same error.  The updated firmware made sense to try, but when I attempted the update I received the following errors:

 

Unable to update device  with Boot Monitor, stopping all further processing of this device!
Firmware distribution does not match target device platform; this could be due to a corrupt distribution.

 

Are you aware of another solution I should try or a different firmware I may need? My setup is as follows:

 

Model: Smart-UPS 1000
SKU: SMT1000
Firmware Revision: UPS 09.3 (ID18)

Model Number: AP9630
Hardware Revision: 05

Application Module
Name: sumx
Version: v6.6.4

APC OS (AOS)
Name: aos
Version: v6.6.4

APC Boot Monitor
Name: bootmon
Version: v1.0.8

 

Thanks for any insight you can provide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore