Send InviteCancel
Posted: ‎2025-09-1202:28 AM
SRVPM3KRIL-E self-test aborted
Hi everyone, i had encounter an issue my UPS model SRVPM3KRIL-E self-test aborted when i run test via NMC portal. I also check the event log and it not show any reason due to self test aborted. While i run via display button, it show passed but the self test result not recorded at event log. Any suggestion or solution to encountering this issue?
Posted: ‎2025-09-1207:03 AM
You will need to provide the serial number of the UPS. Along with the production date of the RBC and installation date as seen on the LCD / NMC.
Generally speaking a failed Self Test indicates a end of life (EOL) RBC (Replacement Battery Cartridge).
The average service life is 2-5 years based on usage, temperature, and environmental conditions.
The RBC can sustain 260 full depletion cycles before degradation is seen. You may see in the logs / emails where the system declares a message like *the load cannot be supported* at some point etc.
You can quickly test this out by conducting a Lights Out / Grid Down event by removing AC Mains from the unit.
There are three possible scenarios which are immediate shutdown and drop in load. To shutdown in a very short period say 1-3 minutes.
To observing 50% less operational runtime when compared to a new RBC via the APC Runtime Calculator based on a defined wattage & temperature.
Report back the results of completing a loss of power during a maintenance window. Provide the following logs for review in its entirety: Event, Data, UPS