Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SRT8KRMXLI - bypass max. 16A?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT8KRMXLI - bypass max. 16A?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS On-Line

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
do1212
do1212
Cadet

Posted: ‎2025-03-02 03:20 PM . Last Modified: ‎2025-03-02 03:21 PM

0 Likes
0
469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 03:20 PM . Last Modified: ‎2025-03-02 03:21 PM

SRT8KRMXLI - bypass max. 16A?

TLDR: Is there a way to prevent the UPS to draw more than 16A even if in bypass mode?


yesterday i had some bigger trouble installing a new UPS

Note that this is a german installation, so the 8kVA online UPS is fed by 230VAC 3-phase 16A input

50Hz input, 50Hz output

I burned through two or three breakers wich caused a major unplanned downtime at our customer
I'm not an electrician so all the hardwiring was done by an external electrician.

1. The first mistake was, we overlooked the phase bridge was still mounted and that was when the first breaker burned through.
2. We then noticed that only one of the three outlet groups was delivering power. I restarted all outlet groups including the working one while there was a load attached (approx. 650VA) wich burned antother breaker. And i don't know why. Of course, restarting outlets with attached load is not ideal but the load was not so high it should cause events like this.
The UPS also wrote down an internal error wich caused it to switch to bypass mode, also not understanable for me. The next event said "switching to battery power due to distorted input" wich is expectable because one of the three pahses was down

The problem is the breaker design for the room. There are 6 circuits in the server room: F5.1.1 to F5.1.6.
F5.1.1, F5.1.2, F5.1.3 are the three phase input for the UPS, the other three are single phase normal input, each one 16A.
But that were not the breakers burning through.
F5.1.1 and F5.1.4 are both L1, .2 and .5 are L2, .3 and .6 are L3.
After those first breakers is a second row of breaker, for each phase a 35A-breaker. These ones got burned through. Don't know why.

The electrician assumed there was a too high current on L1. This with the fact that the UPS protocolled a temporary bypass made me think.
In normal operation the UPS does not draw moer than 16A from a single phae and we only have 16A-breakers as first instance (the 35A as second instance)
Is there a way to prevent the UPS to draw more than 16A even if in bypass mode? Or completely disable bypass mode if the load is too high?
Does the setting "Bypass Transfer Mode" have any infuence on this?
Does this kind of UPS usually go to bypass if the batteries are changed?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • deutsch
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore