No Power on some Outlet Groups (SRT8KRMXLI)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No Power on some Outlet Groups (SRT8KRMXLI)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Related Products
product field
Schneider Electric
Smart-UPS On-Line

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
do1212
do1212
Cadet

Posted: ‎2025-03-02 03:09 PM . Last Modified: ‎2025-03-02 03:10 PM

0 Likes
0
109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 03:09 PM . Last Modified: ‎2025-03-02 03:10 PM

No Power on some Outlet Groups (SRT8KRMXLI)

TLDR: SRT8kRMXLI, 3phase 230V input, only outlet group 2 ist working, not one and three - any advice?

 

yesterday i had some bigger trouble installing a new UPS

Note that this is a german installation, so the 8kVA online UPS is fed by 230VAC 3-phase 16A input

I burned through two or three breakers wich caused a major unplanned downtime at our customer
I'm not an electrician so all the hardwiring was done by an external electrician.

1. The first mistake was, we overlooked the phase bridge was still mounted and that was when the first breaker burned through.
2. We then noticed that only one of the three outlet groups was delivering power. I restarted all outlet groups including the working one while there was a load attached (approx. 650VA) wich burned antother breaker. And i don't know why. Of course, restarting outlets with attached load is not ideal but the load was not so high it should cause events like this.
The UPS also wrote down an internal error wich caused it to switch to bypass mode, also not understanable for me. The next event said "switching to battery power due to distorted input" wich is expectable because one of the three pahses was down

The problem is the breaker design for the room. There are 6 circuits in the server room: F5.1.1 to F5.1.6.
F5.1.1, F5.1.2, F5.1.3 are the three phase input for the UPS, the other three are single phase normal input, each one 16A.
But that were not the breakers burning through.
F5.1.1 and F5.1.4 are both L1, .2 and .5 are L2, .3 and .6 are L3.
After those first breakers is a second row of breaker, for each phase a 35A-breaker. These ones got burned through. Don't know why.

After the electrician switched the breaker, we restartet outlet group 1 and 3 again. Still no power. Only outlet group 2 is working.
Any idea why only one outlet group is working?
This makes technically no sense as internally, the UPS is just a single pahse...

I still have check if the circuit breakers of the singel outlet groups hav tripped, but why should they have tripped? There was never a load more than 5A / 1100W on those outlet groups. Also why is Group two then still working?
Of course i will also contact APC support on that issue.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • deutsch
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of