SRT5kXLT as backup for well pump

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT5kXLT as backup for well pump
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
2
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

SRT5kXLT as backup for well pump

Hi Everyone,

I have an SRT5KXLT which i would like to use as an emergency backup for a 220v well pump.  The well pump is rated at 1.1kw.  it will be direct wired to a manual transfer switch - essentially taking the place of a generator.  I'm basically using the UPS as an inverter and battery bank.  I have a few questions and I'm looking for help and feedback. Appreciate any advice in advance!

The UPS has input wiring of L1, L2, and Neutral/ground.  I know that neutral is bonded to ground at my main panel.  

1) Should the input wiring be L1, L2, and neutral or L1, L2, and ground?  (I believe it should be neutral but would like confirmation)

2) The output on the UPS is three prongs.  is it also L1, L2, and neutral?  

3) My transfer switch is connected to the main panel with 220V, including neutral and ground.  When i switch to UPS supplied power, and the UPS didn't provide a ground, then i am now using the main panel ground but with UPS supplied L1, L2, and neutral.  Is this an issue? should I be grounding the UPS chassis ground screws to my main panel ground?

Thanks,

Michael

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

thanks Liam.  I am mostly concerned about the unbalanced output impact on the motor.  (apparently unbalanced voltages can lead to windings overheating)

If I use the APC isolation transformer will that ensure balanced output on the 240v transformer output?  i.e. could I take the 240v output from the SURT003 L14-30R connector, run it to a panel and split it into two separate 120v circuits.?  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

Hi Michael,

The input and output of this UPS is L1, L2, Ground. There is no neutral. It will default to 208v and can be configured to 240v, but not to 220v. If you are in the US, you likely have 240v and not 220v as you indicated. One thing to note - when this UPS is on battery it will output 208v (or 240V) when you measure from L1 to L2, but it will not be 2 balanced legs of 120v as you might expect. While on battery this unbalanced ouput could be 120v on one leg and 88v on the other, or any other combination that adds up to 208v (or 240v) from L1 to L2. The UPS is designed with IT environments in mind and not motor loads. You may want to consult with your pump vendor to ensure that this won't be an issue.

If you require a balanced output you would need an isolation/stepdown transformer on the output of the UPS.

I would suggest the SRT5KTF:

http://www.apc.com/shop/tt/en/products/APC-Smart-UPS-SRT-5kVA-Tower-Isolation-Step-Down-Transformer/...

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

0 Likes
0
834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:12 AM . Last Modified: ‎2024-03-18 12:02 AM

thanks Liam.  I am mostly concerned about the unbalanced output impact on the motor.  (apparently unbalanced voltages can lead to windings overheating)

If I use the APC isolation transformer will that ensure balanced output on the 240v transformer output?  i.e. could I take the 240v output from the SURT003 L14-30R connector, run it to a panel and split it into two separate 120v circuits.?  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore