Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

SRT3000XLI Output Overload and Bypass Behavior

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT3000XLI Output Overload and Bypass Behavior
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
mike11
mike11
Cadet

Posted: ‎2022-02-14 04:11 AM

0 Likes
3
2967
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-14 04:11 AM

SRT3000XLI Output Overload and Bypass Behavior

Hi, we're occasionally getting the following error on the controller of a Smart-UPS On-Line, model SRT3000XLI: "Output Overload. Backup Not Available". Underneath the message where it shows the operating mode, it shows this as "Online". However, the system is being used by a 3rd party in a remote location on our behalf, so it's not clear if the text changes between the error occurring and the operator spotting it. The unit is not network connected to retrieve logs for further diagnosis.

 

I suspect the cause of the overload is start-up in-rush current draw by the equipment connected to the UPS. From the error message, is it possible to understand what the UPS did when it experienced the overload? Below are a few possibilities I can think of but I can't work out from the user manual which it is for certain.

 

1. The UPS continued powering the load during the overload and this was achieved by drawing extra current from the UPS battery

2. The UPS continued powering the load during the overload but went into automatic Bypass mode to do this - i.e. it passed the UPS mains input through to the output for the duration of the overload and then went back to the normal Online mode.

3. The UPS stopped powering the load during the overload/outputted a voltage below the lower acceptable limit

 

Thanks,

Mike

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-16 12:34 AM

0 Likes
2
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-16 12:34 AM

Hello Mike

 

Many units are designed with a bit of overhead in regard to overload, when input power is good and the unit is running normally.

But, for many units, the overhead is not available when running of it's battery and inverter.

 

So, if indeed you are looking at shorter in-rush currents, you could be in that overhead.

That situation would cause the unit to inform you that it is overloaded, but since you are in the overhead it is still in online mode. But, at the same time, the lack of overhead when running of the battery leads to the "Backup not available" part of the message.

 

If the unit looses input power at the exact moment of your inrush, the backup is not available and the unit will stop powering the load.

 

I hope the above makes sense, and if that is the case I would ask, that you mark the post as solved.

 

 

Best regards

Tonny

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mike11
mike11
Cadet

Posted: ‎2022-02-17 02:11 AM

In response to TonKei
0 Likes
1
2922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-17 02:11 AM

Hello Tonny,
Thanks for your explanation. I have some follow up questions:

1. When the scenario "Output Overload. Backup Not Available. Online" occurs, am I right in saying that all the power for the load comes through the following path: mains AC -> UPS DC -> UPS AC -> load? I.e. not: mains AC -> UPS DC + UPS battery DC -> UPS AC -> load. And not bypassing the AC-DC-AC conversion: mains AC -> (UPS bypass) -> load.

2. When the scenario "Output Overload. Backup Not Available. Online" occurs, I expect the voltage at the UPS output supplying the load will fluctuate a bit. In the manual, the spec given is: AC output dynamic voltage regulation: < ± 2% rms of the initial value. Load Step: 10% to/from 90% resistive load. The in-rush current is caused by input capacitors in the load, so it's not purely resistive and given the overload, the change at turn on will be >100%. So I expect the UPS output voltage could vary more than ± 2%. My question is, would a warning message appear if the output voltage changes by more than a certain amount? Is there a way to see the output voltage value when this happens - from the display or a log? The metering view that shows the output voltage is replaced by the warning message when the scenario occurs.

3. Is there a way to be completely sure the unit did or didn't go into Bypass mode at any point when the in-rush current occurred? E.g. if for most of the time of the in-rush the UPS stayed in Online mode but for a short instant it went into Bypass mode. Would the screen update to show that? Or can it be seen on a log?

Thanks,
Mike

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2022-02-17 04:49 AM

In response to mike11
0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-17 04:49 AM

Hi Mike

 

We actually have a white paper on the different UPS topologies, and if you look at page 7, the double conversion on-line topology is explained in a bit more detail.

-> https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SADE-5TNM3Y_EN

 

As to the output power quality when the unit is running in its overhead window: The UPS is designed based on a hierarchy of priorities. The top one of these being that the unit should at all time deliver good quality power to the load attached. So, if the unit measures that the output power goes beyond the acceptable range, it will seize delivering power. in other words even when you are in the "overhead" you should be receiving the same quality of power as when you are in normal running mode. 

 

You should be able to see the latest 10 times the unit has changed in and out of online mode in the transfer log in the display.

But, for more detailed logging, a network management card is really helpful. It provides a ongoing log that is stored on the card, so it is available even if the card does not have network connection all the time.

 

Best regards

Tonny

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of