Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SRT2200XLI
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3007:31 AM. Last Modified: 2024-03-0711:00 PM
Hi Manuel,
In typical 3 wire L-N-G environments the neutral normally carries current back to the source and is usually connected to ground at the main electrical panel, and also at the final step-down transformer of the supply. As such, care must be taken that the neutral conductor never rises to a high voltage with respect to local ground. Connecting the L-N-G input of the UPS to a 2P+G supply would result in having to connect the UPS neutral to either L1 or L2 of the supply circuit, but using the live would still not substitute the function of neutral, so connecting this UPS to a 2P+N supply is not recommended or approved.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3007:31 AM. Last Modified: 2024-03-0711:00 PM
Hi Manuel,
In typical 3 wire L-N-G environments the neutral normally carries current back to the source and is usually connected to ground at the main electrical panel, and also at the final step-down transformer of the supply. As such, care must be taken that the neutral conductor never rises to a high voltage with respect to local ground. Connecting the L-N-G input of the UPS to a 2P+G supply would result in having to connect the UPS neutral to either L1 or L2 of the supply circuit, but using the live would still not substitute the function of neutral, so connecting this UPS to a 2P+N supply is not recommended or approved.