SRT2200XLI firmware update failed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT2200XLI firmware update failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:46 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
4
2196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:46 AM . Last Modified: β€Ž2024-03-15 04:21 AM

SRT2200XLI firmware update failed

Hello,

I'm stuck because of upgrade failure on the UPS. In the Web GUI, many values are set to 0.

UPS firmware : 05.3 (ID1010)
AP9630 firmware : 6.9.4

I'm able to connect to the web GUI but I can't upgrade because it says that UPS is not off. But the GUI only let me to Power On the UPS.
I'm able to connect using Putty (SSH) ou Filezilla (FTP).
I"ve downloaded the latest firmware : SRT1010UPS_07-9.enc

When I try to upload it using Filezilla, I've an error during transfer at about 600 Ko :

Status: Starting upload of C:\temp\SRT1010UPS_07-9.enc
Status: Retrieving directory listing of "/"...
Command: PASV
Response: 227 Entering Passive Mode (172,30,33,251,235,67).
Command: LIST
Response: 150 File status okay; about to open data connection.
Response: 226 Closing data connection.
Command: PASV
Response: 227 Entering Passive Mode (172,30,33,251,130,35).
Command: APPE SRT1010UPS_07-9.enc
Response: 502 APPE command not implemented, or not allowed.
Error: Critical file transfer error after transferring 1,024 bytes in 1 second

What can I do to upgrade the UPS ?

Thanks,

Vincent

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • firmware
  • upgrade
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
0
2194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

Hello,

I tried with the DB9 cable and run the 4.2.1 FirmwareUpgradeWizard.

the UPS is found on COM3:
UPS : 05.3
COM : 05.2
CBL : 01.2

the new firmware detected is : SRT1010UPS_08-3

I have an error during the upgrade process (see screenshot).

Houston ? We have a problem 😞

Thanks for help,

Vincent

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:46 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:46 AM . Last Modified: β€Ž2024-03-15 04:21 AM

Hi Vincent,

It looks like you've might have things a little mixed up, the process your following via FTP is to update the management card not the ups but the file your trying to copy is the UPS firmware.

See below to update a UPS:

https://www.apc.com/us/en/faqs/FA164737/

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

oh ok, so, there's no way to update the UPS throw FTP or SSH ? I have to switch to DB9 ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
0
2193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

The official recommendation is to do it locally via DB9 even when other options are available and I would personally agree with that. It's the most reliable and it can be hard to recover a UPS after a failed firmware update.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

0 Likes
0
2195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 11:47 AM . Last Modified: β€Ž2024-03-15 04:21 AM

Hello,

I tried with the DB9 cable and run the 4.2.1 FirmwareUpgradeWizard.

the UPS is found on COM3:
UPS : 05.3
COM : 05.2
CBL : 01.2

the new firmware detected is : SRT1010UPS_08-3

I have an error during the upgrade process (see screenshot).

Houston ? We have a problem 😞

Thanks for help,

Vincent

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore