SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
Brumm
Crewman
Crewman
0 Likes
12
1257

SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

We installed a SRT1500RMXLI-NC just yesterday and I observed a couple of these messages in the logs:

 

 

 

05/12/2022	09:11:14	Device	UPS: RFC1628 MIB alarm entry removed.	0x3605
05/12/2022	09:11:14	Device	UPS: Return from bypass, internal hardware fault no longer present.	0x01B2
05/12/2022	09:11:14	Device	UPS: RFC1628 MIB alarm entry added.	0x3604
05/12/2022	09:11:14	Device	UPS: In bypass in response to an internal hardware fault.	0x011B
05/12/2022	03:35:38	Device	UPS: RFC1628 MIB alarm entry removed.	0x3605
05/12/2022	03:35:38	Device	UPS: Return from bypass, internal hardware fault no longer present.	0x01B2
05/12/2022	03:35:38	Device	UPS: RFC1628 MIB alarm entry added.	0x3604
05/12/2022	03:35:38	Device	UPS: In bypass in response to an internal hardware fault.	0x011B
05/12/2022	01:43:19	Device	UPS: RFC1628 MIB alarm entry removed.	0x3605
05/12/2022	01:43:19	Device	UPS: Return from bypass, internal hardware fault no longer present.	0x01B2
05/12/2022	01:43:18	Device	UPS: RFC1628 MIB alarm entry added.	0x3604
05/12/2022	01:43:18	Device	UPS: In bypass in response to an internal hardware fault.	0x011B
05/12/2022	00:07:42	Device	UPS: RFC1628 MIB alarm entry removed.	0x3605
05/12/2022	00:07:42	Device	UPS: Return from bypass, internal hardware fault no longer present.	0x01B2
05/12/2022	00:07:41	Device	UPS: RFC1628 MIB alarm entry added.	0x3604
05/12/2022	00:07:41	Device	UPS: In bypass in response to an internal hardware fault.	0x011B

 

 

 

These are the most recent entries in the logs. There were two more occurences of this yesterday afternoon. It seems that this internal hardware fault is only occuring for a very short period. What should I do? Is that something to worry about?

Tags (1)

Accepted Solutions
exHPguy
Ensign
Ensign
2
1126

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

On my issue, I downgraded the network cards firmware and the problem went away

See Answer In Context

Tags (1)
exHPguy
Ensign
Ensign
0 Likes
0
1012

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Same with me

 

Downgrading the AP9640 network card from 2.2.0.1  to 2.0.0.5 fixed the issue.

See Answer In Context

Tags (1)
12 Replies 12
exHPguy
Ensign
Ensign
0
1185

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

I have a couple of SRT 3000s that just started with that error also

 

Critical - UPS: In bypass in response to an internal hardware fault.

 

then one second later

 

Informational - UPS: Return from bypass, internal hardware fault no longer present.

Tags (1)
Brumm
Crewman
Crewman
0 Likes
4
1148

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

A small update: I observed the logs of the last days. And these error messages keep appearing every couple of hours (so 5 -10 per day). This is really annoying as it clutters the event log. Is there anything to do about it?

Tags (1)
exHPguy
Ensign
Ensign
2
1127

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

On my issue, I downgraded the network cards firmware and the problem went away

Tags (1)
jfrancis
Cadet
0 Likes
1
1030

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Interesting...

 

This error started after I upgraded the firmware on my PowerChute Network Management Card 3. 

Tags (1)
exHPguy
Ensign
Ensign
0 Likes
0
1013

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Same with me

 

Downgrading the AP9640 network card from 2.2.0.1  to 2.0.0.5 fixed the issue.

Tags (1)
jfrancis
Cadet
0 Likes
0
997

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

@exHPguy Thanks, as per your experience, I downgraded as well to resolve the problem.

Tags (1)
mkuhn22
Ensign
Ensign
0 Likes
5
951

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

To add to this I can also confirm that after updating ~10 AP9640s to the 2.2.0.1 firmware and within 24 hours every one of them started throwing "In bypass in response to an internal hardware error.", with a return to normal state within the same second.  As mentioned in thread downgrading back to the 2.0.0.5 firmware has resolved the issue on all 10 devices.

 

Thanks, @exHPguy 

Tags (1)
Brumm
Crewman
Crewman
0 Likes
4
892

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Thanks, for all the replies. I was hoping to solve my issue, but where do I get the old version of the Firmware? I only seem to find v2.2.0.1 on https://www.apc.com/us/en/download/document/APC_NMC3_SU_2201_EN/ and that's what I have already.

Tags (1)
mkuhn22
Ensign
Ensign
0 Likes
0
885

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

You may be able to reach out to support for it directly.  I know when I had to bring an old Struxureware install to current they provided me with direct links to some of the step upgrades I'd need that aren't available on the site via links any longer.  In this case I happened to still have my 2.0.0.5 download handy which is how I stepped back.  It'd be nice if they didn't remove previous versions once they mark them "obsolete".  Right here's a pretty clear example of a reason to keep at least one additional version available to download.

Tags (1)
JonPro
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
862

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Hi @Brumm,

 

Please share your email address via DM and I will send you the file.

Regards,

JonPro
Secure Power Team
Tags (1)
Brumm
Crewman
Crewman
0 Likes
1
701

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

As others mentioned already, this solved the problem for me.

Tags (1)
BillP
Administrator Administrator
Administrator

Re: SRT1500RMXLI-NC: In bypass in response to an internal hardware fault.

Tags (1)