SRT10K - which battery is which? Internal Battery Pack 2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT10K - which battery is which? Internal Battery Pack 2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-22 08:33 AM

0 Likes
9
1238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 08:33 AM

SRT10K - which battery is which? Internal Battery Pack 2

Good day all, 

I have an SRT10K with extra battery backs - and I've received a warning that the "Internal battery pack" (or "near end of life - 02, 02" on the front LED panel)

NMC Battery status warning: 

  • Battery near end of life. Order replacement battery, APCRBC140, for the internal pack, cartridge 1.
  • Battery near end of life. Order replacement battery, APCRBC140, for the internal pack, cartridge 2.

There are 4 physical batteries in the "internal" section - so I replaced the pair on the left, as the 2 arrow indicates.

Are those cartridges 1 & 2? But in NMC there's only 2 listed - not 4.

JWCCC_0-1758555093000.png

Does it mean all 4 need to be replaced soon (expected) - or just #2?

I'm confused by the LED panel warning - feels very specific to pack-pair 2, so that's what I replaced.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-25 05:49 AM

In response to Teken
0 Likes
0
1145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-25 05:49 AM

Well, it says "The UPS may not immediately report that a battery cartridge has been disconnected". I didn't expect it to fail to detect hours later.  

The good news is, it was detected when it performed a self-check. 

JWCCC_0-1758804569550.png

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-23 06:21 AM

0 Likes
5
1233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-23 06:21 AM

Disconnect the RBC pairs and monitor via LCD / NMC. It will tell you which pair is missing.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-23 08:46 PM

In response to Teken
0 Likes
4
1215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-23 08:46 PM

Unfortunately, with low load it may not. Known issue. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-24 04:44 AM

In response to JWCCC
0 Likes
3
1207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 04:44 AM

If you disconnect the RBC pairs the system will declare a battery fault. Using the LCD Panel / NMC you can see this.

 

At that point you’ll know which module requires a RBC replacement.


I’m assuming the RBC date is incorrect otherwise why wouldn’t you refer to that also??

Reply

Link copied. Please paste this link to share this article on your social media post.

JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-24 05:49 AM

In response to Teken
0 Likes
2
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 05:49 AM

RBC date is correct - as it was confirmed/set when it was installed.   Not sure why or how that would tell me if it was all OEM and all dates are same.

I will try the removal method, but longer, and see it it flags - because when I swapped out #2 for new ones - it did not indicate battery was removed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-24 06:27 AM . Last Modified: ‎2025-09-24 07:04 AM

In response to JWCCC
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 06:27 AM . Last Modified: ‎2025-09-24 07:04 AM

Show me the battery tab via NMC for both RBC.  Provide a screen capture from the NMC under About for both UPS / NMC.

 

If the RBC are the original ones from the factory that were installed. Than the error declared for an end of life (EOL) RBC applies to all four cartridges. 

Meaning all four must be replaced . . . 

The average service life is 2-5 years based on usage, temperature, and environmental conditions. The cells are designed to endure 260 full cycles before signs of degradation.

When the RBC’s are disconnected the system will declare a battery disconnected / missing fault / error.

 

Wait for this to happen before you proceed. Once that message appears you would install the new RBC and connect the Anderson connectors. 

At that point the system will prompt you to confirm if this is a new RBC. Toggle from No to Yes and enter than enter the month and year of the installation date.

 

Next manually initiate a self test and let pass and wait for the RBC’s to return to 100% SOC.

 

Complete the procedure by manually initiating a Battery Calibration with a minimum of 30% attached load or greater.

 

Once this procedure has completed allow the RBC’s to recover to 100% SOC. This will insure the LCD, NMC, SNMP, Power Chute will more accurately reflect the operational runtime of the system. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-24 07:57 AM

In response to JWCCC
0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 07:57 AM

I've disconnected the battery - and an hour later, still no warning.

Reply

Link copied. Please paste this link to share this article on your social media post.

JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-24 08:06 AM

0 Likes
2
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-24 08:06 AM

I am aware of the general useful life - I'm not surprised it's come throwing the warning. 

 

I disconnected the UPS around 10:15am.  As of these screenshots at 11am, it has not detected its removal.

I believe this is the cause: SRT Battery Detection | Schneider Electric Australia (though I'm not in AUS)

 

Overall battery status page:

JWCCC_0-1758726001056.png

Internal pack page: (I haven't set the date yet, because I haven't determined for sure, which it was)

JWCCC_1-1758726017240.png

 

NMC about:

JWCCC_2-1758726057996.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-25 03:02 AM

In response to JWCCC
0 Likes
1
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-25 03:02 AM

Have you tried the action items called out by this FAQ?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

JWCCC
Crewman JWCCC
Crewman

Posted: ‎2025-09-25 05:49 AM

In response to Teken
0 Likes
0
1146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-25 05:49 AM

Well, it says "The UPS may not immediately report that a battery cartridge has been disconnected". I didn't expect it to fail to detect hours later.  

The good news is, it was detected when it performed a self-check. 

JWCCC_0-1758804569550.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore