We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 08:12 AM . Last Modified: 2024-03-07 03:23 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:12 AM . Last Modified: 2024-03-07 03:23 AM
Kind greetings! May I use the parallel kit SRCPK001 on two tower SRT6KXLI units? (redundancy purposes). I saw a post mentioning its use on SRC models only...
If not possible, which would be the right way to connect the redundantly? Thank you for your kind advice!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:13 AM . Last Modified: 2024-03-07 03:23 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:13 AM . Last Modified: 2024-03-07 03:23 AM
Thank you for your prompt reply, Bill.... I went through the Application Note 98 and it solely refers to a server backup scenario. What I'm trying to protect is a delicate science lab instrument, where I won't have a Powerchute software controlling the UPSs. What are my options? Choose SRC units instead, in spite of being "budget" alternatives?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:13 AM . Last Modified: 2024-03-07 03:23 AM
Hi,
The kit is not compatible with SRT model Smart-UPS. You can pair SRT Smart-UPS in redundant fashion with PowerChute Network Shutdown. See Application Note 98.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:13 AM . Last Modified: 2024-03-07 03:23 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:13 AM . Last Modified: 2024-03-07 03:23 AM
Thank you for your prompt reply, Bill.... I went through the Application Note 98 and it solely refers to a server backup scenario. What I'm trying to protect is a delicate science lab instrument, where I won't have a Powerchute software controlling the UPSs. What are my options? Choose SRC units instead, in spite of being "budget" alternatives?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of