Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SRC3000XLI New Battery Replaced But Runtime Remaining Same.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-08-1211:41 PM
SRC3000XLI New Battery Replaced But Runtime Remaining Same.
Hello,
I am Using APC SRC3000XLI. Recently I replaced full set (8 units) battery due to low runtime. But Even after replacing battery , the runtime remain same.
I have other ups with same model. those ups showed long Runtime with same battery & same load. Only Said UPS Showing low runtime.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-08-1303:50 AM
The following steps outlined below must be done upon battery replacement if available and present:
Battery Installation: Date must be updated as this will reset internal counters adjust charging tables if applicable.
Self Test: Manually initiate a self test and let pass and allow the battery to return to 100% SOC.
Battery Calibration: Manually initiate a calibration with at least 30% attached load. Once completed allow the RBC to recover and recharge back to 100% SOC.
The operational runtime displayed will now be more accurate on the LCD, NMC, PCSS, SNMP.