SNMP Resets @4min on a 2.2kva

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMP Resets @4min on a 2.2kva
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
8
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

SNMP Resets @4min on a 2.2kva

Installed a good working AP9619 into a 2200 XL, the card reset every 5 minutes. Tried two different ones, same result. The cards work perfectly in other UPSs. Could this be a UPS fault?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:50 AM

Will get back to you with a full log shortly. This only happens on one particular UPS, every 4 minutes. It goes in a circle and never stops. No other events happening. The card has been tested in our other units and no such thing occurs. Will report back with firmware and full log

Thank you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

What's the exact message in the event logs, does it say that the card warm starts? Can you also tell us what the firmware of the card and what software do you use in monitoring the card via SNMP?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

If you need help downloading those files BTahimic asked for, refer to the knowledge base @ http://www.apc.com/site/support/index.cfm/faq/ and search for article ID FA156131 - as was mentioned, we need more information on the actual events logged. Once we have that, we can make a better recommendation for a resolution.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

Will run it for a few hours and upload the logs here soon! Thank you for the prompt responses!

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:51 AM

Here's the basic log, if more is needed let me know please.

192.168.2.13 [local3.emerg] APC:]# Test Syslog.

192.168.2.13 [local3.crit] System:]# Warmstart. 0x0002

192.168.2.13 [local3.info] UPS:]# Restored the local network management interface-to-UPS communication. 0x0101


Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

Here's the basic log, if more is needed let me know please.

192.168.2.13 [local3.emerg] APC:]# Test Syslog.

192.168.2.13 [local3.crit] System:]# Warmstart. 0x0002

192.168.2.13 [local3.info] UPS:]# Restored the local network management interface-to-UPS communication. 0x0101


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

OK - can you tell me what firmware versions are on this card and let me know how often you are seeing this? i'd be helpful to see the full log to see if any other events are happening before/after that are contributing to this.

We have some information in the knowledge base about this for reference -> FAQ and search for FA156063

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:35 AM . Last Modified: ‎2024-03-13 12:50 AM

No problem - depending on what I see, we may suggest an update or a reset to defaults on the card if it is at the latest already. Either way, we should be able to address it without issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:50 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:36 AM . Last Modified: ‎2024-03-13 12:50 AM

Will get back to you with a full log shortly. This only happens on one particular UPS, every 4 minutes. It goes in a circle and never stops. No other events happening. The card has been tested in our other units and no such thing occurs. Will report back with firmware and full log

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore