Hello, I try to monitor by snmp 4 PDU AP8853. I have downloaded the mib and look at the manual but... there is so many oid ! I have tried many oid but I have not found what I need : I only need 3 most important oid to get the following values (witch we can see in the web homepage) :
- Device Load (KW),
- Phase L1 Load (A)
- Bank 1 Load (A)
- Bank 2 Load (A)
Can anyone help me ?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:25 PM . Last Modified: 2024-03-12 12:53 AM
Hi Fabien,
Yes, you're right, there are many OIDs. I suggest you start by downloading a MIB browser such as GetIf or iReasoning to browse the MIB to make it easier. All of the OIDs for AP8XXX series PDU models like yours are here in the tree: iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26)
Below should be what you're looking for but you can double check in a MIB browser like I just did.. read the names/descriptions of the OIDs.
On 11/17/2017 12:25 PM, Fabien said:- Device Load (KW),
1.3.6.1.4.1.318.1.1.26.4.3.1.5
On 11/17/2017 12:25 PM, Fabien said:- Phase L1 Load (A)
1.3.6.1.4.1.318.1.1.26.6.3.1.5
On 11/17/2017 12:25 PM, Fabien said:- Bank 1 Load (A)
On 11/17/2017 12:25 PM, Fabien said:- Bank 2 Load (A)
This should be 1.3.6.1.4.1.318.1.1.26.8.3.1.5 and it will respond twice (two instances) for each bank. You can confirm this is bank1/bank2 if you read 1.3.6.1.4.1.318.1.1.26.8.3.1.3 first which will confirm which banks its reading. (should be a response of 1 and 2 for bank1/bank2.
Hope that helps you get started. You can also walk the MIB to see what responds in general and see what's available.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:25 PM . Last Modified: 2024-03-12 12:53 AM
Hi Fabien,
Yes, you're right, there are many OIDs. I suggest you start by downloading a MIB browser such as GetIf or iReasoning to browse the MIB to make it easier. All of the OIDs for AP8XXX series PDU models like yours are here in the tree: iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26)
Below should be what you're looking for but you can double check in a MIB browser like I just did.. read the names/descriptions of the OIDs.
On 11/17/2017 12:25 PM, Fabien said:- Device Load (KW),
1.3.6.1.4.1.318.1.1.26.4.3.1.5
On 11/17/2017 12:25 PM, Fabien said:- Phase L1 Load (A)
1.3.6.1.4.1.318.1.1.26.6.3.1.5
On 11/17/2017 12:25 PM, Fabien said:- Bank 1 Load (A)
On 11/17/2017 12:25 PM, Fabien said:- Bank 2 Load (A)
This should be 1.3.6.1.4.1.318.1.1.26.8.3.1.5 and it will respond twice (two instances) for each bank. You can confirm this is bank1/bank2 if you read 1.3.6.1.4.1.318.1.1.26.8.3.1.3 first which will confirm which banks its reading. (should be a response of 1 and 2 for bank1/bank2.
Hope that helps you get started. You can also walk the MIB to see what responds in general and see what's available.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:25 PM . Last Modified: 2024-03-12 12:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:25 PM . Last Modified: 2024-03-12 12:53 AM
Thank you very much ! It works.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-12 12:52 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-19 10:19 PM
from where can i download the MIB for AP8853?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-17 12:06 PM
could you please share with me the voltage oid