SMX750C Fan

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX750C Fan
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
jwood_ok
Crewman jwood_ok
Crewman

Posted: โ€Ž2025-07-02 08:58 AM

0 Likes
3
468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-02 08:58 AM

SMX750C Fan

Hello,

 

I was taking a look at a couple of SMX750C's and noticed that the fan was not turning on one of them.  I then looked at another and found the same thing.  Initially I thought something was wrong, but since I've run into this twice, I'm wondering if the fan does not run all the time, but only kicks in when cooling needs to take place, and I wanted to verify that.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-07-02 11:51 PM

0 Likes
2
467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-02 11:51 PM

The fan will come on during the following conditions / reasons:

 

Upon first start up, loss of AC Mains, over heat condition, recharging. Depending upon what version of UPS firmware it will also come on during an update.

 

The system has two fan speeds even though itโ€™s not a 4 wire PWM vs 2 wire fan.


NOTE: The system tracks if and when these conditions are present / happened in the Event / UPS logs.

 

Unplugging the fan will cause the system to declare a fan error. An internal over heat condition whether battery / system will declare an active fault / condition.

 

Questions Ask - If not, and this answered your query please consider marking this reply as a solution to help the next person asking the same . . . ๐Ÿ‘

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-07-02 11:51 PM

0 Likes
2
468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-02 11:51 PM

The fan will come on during the following conditions / reasons:

 

Upon first start up, loss of AC Mains, over heat condition, recharging. Depending upon what version of UPS firmware it will also come on during an update.

 

The system has two fan speeds even though itโ€™s not a 4 wire PWM vs 2 wire fan.


NOTE: The system tracks if and when these conditions are present / happened in the Event / UPS logs.

 

Unplugging the fan will cause the system to declare a fan error. An internal over heat condition whether battery / system will declare an active fault / condition.

 

Questions Ask - If not, and this answered your query please consider marking this reply as a solution to help the next person asking the same . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

jwood_ok
Crewman jwood_ok
Crewman

Posted: โ€Ž2025-07-03 11:17 AM

In response to Teken
0 Likes
1
419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-03 11:17 AM

Thank you - so in otherwords, the fan does not run constantly, only in certain conditions, so there's not necessarily anything unusual about it not running - I was thinking of it more like a power supply fan that runs all the time, which is why I was initially concerned.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-07-07 12:17 AM

In response to jwood_ok
0 Likes
0
416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-07 12:17 AM

Correct, if the previous reply answered your question please mark it as a solution to help the next person asking the same. ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore