SMX3000RMLV2UNC, an old workhorse, suddenly quit working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000RMLV2UNC, an old workhorse, suddenly quit working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
BlueSky
Ensign BlueSky
Ensign

Posted: ‎2024-10-30 09:59 AM

0 Likes
6
1127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-30 09:59 AM

SMX3000RMLV2UNC, an old workhorse, suddenly quit working

My old SMX3000 suddenly quit working.  I powered it off, removed the batteries, moved the UPS gently downstairs, reinstalled the batteries and plugged it into the mains supply and nothing.  Nada.  Zippo.  Bupkiss!  Not even a breath of an attempt to restart.  I tried different known good RBC116/117s with no joy.  Tried different outlets with the same result.  There is no EPO plug installed nor has there ever been.

 

I popped the side off to do a quick visual maybe to spot a burned component or possible a small internal fuse but found nothing.

 

Before I discard it, does anyone have a possible suggestion on where to look for obvious things I overlooked?  I was surprised to find the manual made no mention at all of the two white circuit breakers on the back near the outlet group as a possible fault but found nothing about them.  I suspect they are used to prevent an output overload as they don't seem to be wired into the imput circuitry.

 

Thank in advance for any suggestions!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Kirk Teken
Kirk

Posted: ‎2024-11-04 05:53 AM

1 Like
2
1118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-04 05:53 AM

Is this the same unit you were trying to upgrade the firmware?!? 🤔

Reply

Link copied. Please paste this link to share this article on your social media post.

BlueSky
Ensign BlueSky
Ensign

Posted: ‎2024-11-05 03:10 AM

In response to Teken
0 Likes
1
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-05 03:10 AM

Yes, it is the same unit but the upgrade the firmware was never accomplished because the wizard would not allow the upgrade attempt.  As you mentioned, there was nothing after ID10 v2.0 that I could find.

 

I did scrap the unit and obtained another SMX3000RMLV2UNC from an auction site that was a later build and was at f/w rev level ID1003 v7.6 that I successfully ungraded to v15.0.  The later hardware revision level is much better in that the LCD display can, thankfully, be turned off and the fans only run as necessary.  I also purchased an SMX120RMBP2U from the same vendor so I should be set.

 

Thanks for your assistance in this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-11-05 08:47 AM

0 Likes
0
1077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-05 08:47 AM


What is the battery voltage of the RBC117 cartridge? What is the input line voltage at the NEMA L5-30P outlet as measured by a True RMS DMM?

 

Assuming there is 120 VAC at the outlet when you connect the power cord and the RBC117 is connected. Do you see the battery voltage increase?!?

 

Do you measure any voltage at the outputs? 

Does the system have a NMC if so what happens on the unit when it’s connected to a switch / network when the system is connected to AC Mains?

Reply

Link copied. Please paste this link to share this article on your social media post.

BlueSky
Ensign BlueSky
Ensign

Posted: ‎2024-11-06 02:20 AM

0 Likes
0
1048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-06 02:20 AM

Each of my three RBC117s were right around 135.4 vdc.  My line voltage is around 124 vac as measured with t Fluke 87v true rms dmm.

No the voltage did not increase.

No voltage at the outputs.

NMC2 remained dead, no activity lights, when plugged into the line.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-11-06 07:03 AM

In response to BlueSky
0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-06 07:03 AM

What is the float voltage in this new to you system as displayed on the LCD and measured by your Fluke DMM?!?

 

As an aside this ridiculous (APC Moderation) of holding comments before releasing them. Makes a conversation and trouble shooting 9999999 times harder than it has to be! 🤦‍♂️👎

 

Reading, replies that were posted days ago with ones that are hours later just confuses the entire thread! 🤢👎

Reply

Link copied. Please paste this link to share this article on your social media post.

BlueSky
Ensign BlueSky
Ensign

Posted: ‎2024-11-07 03:40 AM

0 Likes
0
996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 03:40 AM

I agree about the moderation requirements before posting a comment, but I can understand why they do it.  Quite a while ago, there were many posts on this board for offers for form's of identification, university diplomas, etc, that you could order from overseas (outside the US).  I wonder if the moderator, Vartika I believe is the name, is a bot or a real person?  Probably a real person.

 

Regarding the voltages, I could not seem to find the reported voltage from the front panel but the measured voltage with a meter was +135.8 and the voltage reported by the NMC is 136.4.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore