SMX3000RMHV2UNC - An inverter fault exists.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000RMHV2UNC - An inverter fault exists.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
3
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

SMX3000RMHV2UNC - An inverter fault exists.

My SMX3000 UPS has suddenly reported "an inverter fault exists". The panel shows a red LED. The outputs are turned off. The fan is no longer running.

The NMC events log reports are as follows:

Date      Time      User      Event

08.08.2016           15:53:07               Device  UPS: The output power is turned off.

08.08.2016           15:53:07               Device  UPS: An inverter fault exists.

08.08.2016           15:53:06               Device  UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.

08.08.2016           15:53:06               Device  UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.

08.08.2016           15:53:06               Device  UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.

08.08.2016           15:53:05               Device  UPS: Switched outlet group 3, Outlet Group 3, has been commanded to turn on, sequenced.

08.08.2016           15:53:05               Device  UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn on, sequenced.

08.08.2016           15:53:05               Device  UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn on, sequenced.

08.08.2016           15:52:53               Device  UPS: The output power is turned off.

08.08.2016           15:52:53               Device  UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.

08.08.2016           15:52:53               Device  UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.

08.08.2016           15:52:53               Device  UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.

The UPS "about" information is as follows:

Model                                Smart-UPS X 3000

SKU                                  SMX3000RMHV2UNC

Serial Number                    IS1309004233

Firmware Revision               UPS 06.8 (ID23)

Manufacture Date                27.02.2013

Apparent Power Rating         3000  VA

Real Power Rating               2700  W

Internal Battery SKU           APCRBC117

External Battery SKU           APCRBC118

Attempting to reset the UPS by powering off the input feed, removing all batteries, re-installing the batteries and re-applying input power gives the same result - the fan runs briefly, then the UPS shuts down reporting an inverter fault.

Is there anything I can usefully check or reset ?

Cheers, Colin.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • fault
  • inverter
  • smx3000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
0
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

Hello Colin,

I am sorry to hear that you are experiencing issues with your APC unit. Based on your description and the logs you pasted, it looks like there is an inverter fault. That being said, it looks like you completed the "braindead" process, by removing all power sources and load to reset the internal processor. The fact that this did not clear it means, that it is probably not a false positive and the UPS should be replaced asap. After putting the serial number in our system, it looks like it is right around the cusp of being out of factory warranty. I would advise calling into Technical Support at 800 800 4272 and explain to them the fault and what you have done. 

If you have any other questions, please feel free to post them here or ask technical support.

Thanks,

Shanon

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
0
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

Thank you. Support call made. It appears to be a "hard fault". Warranty replacement has been arranged.

Cheers, Colin.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
0
1984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

Hello Colin,

I am sorry to hear that you are experiencing issues with your APC unit. Based on your description and the logs you pasted, it looks like there is an inverter fault. That being said, it looks like you completed the "braindead" process, by removing all power sources and load to reset the internal processor. The fact that this did not clear it means, that it is probably not a false positive and the UPS should be replaced asap. After putting the serial number in our system, it looks like it is right around the cusp of being out of factory warranty. I would advise calling into Technical Support at 800 800 4272 and explain to them the fault and what you have done. 

If you have any other questions, please feel free to post them here or ask technical support.

Thanks,

Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
0
1984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

Thank you. Support call made. It appears to be a "hard fault". Warranty replacement has been arranged.

Cheers, Colin.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

0 Likes
0
1983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:40 PM . Last Modified: ‎2024-03-06 11:52 PM

The UPS has been replaced under warranty. The replacement UPS is working normally. Good service by APC.

Cheers, Colin.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore