SMX3000 - 2U or 4U?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX3000 - 2U or 4U?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
DazOG
Ensign DazOG
Ensign

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
7
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

SMX3000 - 2U or 4U?

Hi,

Hopefully the answer to this is obvious.  I have seen several different SMX3000 units for sale, some of them are 4U, others 2U.  As far as I can make out the runtime without additional battery packs is the same on both units.

Can someone tell me what the differences are between 2U and 4U units?

SMX3000HV - 4U - http://www.apc.com/shop/uk/en/products/APC-Smart-UPS-X-3000VA-Rack-Tower-LCD-200-240V/P-SMX3000HV

SMX3000RMHV2U - 2U - http://www.apc.com/shop/uk/en/products/APC-Smart-UPS-X-3000VA-Rack-Tower-LCD-200-240V/P-SMX3000RMHV2...

There is also another 2U unit with the same capacity?...

SMT3000RMI2U - 2U - http://www.apc.com/shop/uk/en/products/APC-Smart-UPS-3000VA-LCD-RM-2U-230V/P-SMT3000RMI2U

Thanks in advance,

Darren

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DazOG
Ensign DazOG
Ensign

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

Thanks both. 🙂

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

Hi,

U is a unit of measurement. Each U equals 44.45 MM or 1.75 inches.  Check out Schneider Electric FAQ FA158600. 

Reply

Link copied. Please paste this link to share this article on your social media post.

DazOG
Ensign DazOG
Ensign

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

Hi Bill

Sorry, I guess I didn't make myself clear.  I am aware of rack terminology, so I know that 4U is twice the height of 2U.

What I don't understand is why there are two APC SMX3000 SKUs, with the same apparent rating (2700W, 3kVA) in two different sizes.  I would have presumed that the 4U was larger due to more internal cells, or something, but it seems that isn't the case since the runtime on both units for the same wattage is identical.

What I am trying to understand is, why if SMX3000 can exist in a 2U package there is a 4U version at all?

I feel like I am missing something obvious but I haven't been able to establish what that is from the specs alone.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

Hi,

The difference beyond size is the available outlets, price, and replacement battery. 

The 4 U unit offers

(2) IEC 320 C19 (Battery Backup)
(2) IEC Jumpers (Battery Backup)
(8) IEC 320 C13 (Battery Backup)
RBC143

The 2 U
1) IEC 320 C19 (Battery Backup)
(8) IEC 320 C13 (Battery Backup)
(2) IEC Jumpers (Battery Backup)
RBC117
Reply

Link copied. Please paste this link to share this article on your social media post.

DazOG
Ensign DazOG
Ensign

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

So one additional C19 outlet and a different battery type (for some reason?) is the reason one unit is twice the height of the other? 

Sorry I still don't understand this, there must surely be some functional reason besides one additional outlet, otherwise wouldn't everyone choose the cheaper one?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:30 AM

Hi,

If space is not an issue then purchase the 4 U at £1,770.00 If space is an issue then purchase the 2 U at £2,190.00. Or if space is an issue but run-time is not (no need for external batteries) then purchase the SMT 2 U at £1,830.00

You need to decide which model and features are needed and you should take into account what will be needed in the future. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

0 Likes
0
2342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

The 4U unit can be used as a tower as well as rack-mount.

From the specs, the 2U units seem deeper and wider, the 4U unit taller and shallower. The 4U unit might be good for a half-rack.

Reply

Link copied. Please paste this link to share this article on your social media post.

DazOG
Ensign DazOG
Ensign

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:23 AM . Last Modified: ‎2024-03-18 12:29 AM

Thanks both. 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore