SMX1500RM2U with AP9630 "No UPS Found" issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500RM2U with AP9630 "No UPS Found" issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
7
2055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

SMX1500RM2U with AP9630 "No UPS Found" issue

All,

I recently had installed an SMX1500RM2U. I purchased an AP9630 and installed it separately. So far I have not been able to get the NMC to detect the UPS. All I get on the home screen is "No UPS Found". The card came with sumx v6.2.1 firmware and I've since upgraded to sumx v6.4.0 but still the same results. I've brain dead the unit and then reseated the card but still can't get it to detect the UPS. No additional USB or Serial connections are made to the UPS. Any help would be greatly appreciated.


Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9630
  • apc
  • smx1500rm2u
  • sumx
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:57 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:57 AM . Last Modified: ‎2024-03-13 01:10 AM

I contacted support and they sent me a replacement card and all is working well now. The new card recognizes the UPS. 

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

Is the part number written on your AP9630: "640-1110A-Z"?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

Voidstar, thank you for the response. I just pulled the card and it is "640-1110B-Z_REV06"

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

That card should work. If you have other UPSes, you might try swapping the card to see if the problem moves with the card or stays with the UPS. Either way, I'd call APC tech support and see what they can do for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

Lee,

Did you check to make sure you have the right firmware installed?

There are 2 different version of 6.4 firmware depending on what type of UPS the card is going in....

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

Lee,

this one is for the smart UPS

part number: SFSUMX640

link below for the download

http://www.apc.com/vi/en/tools/download/download.cfm?sw_sku=SFSUMX640&software_id=MFOI-A86RLC&family...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:10 AM

Thanks for the response John. Yes I did use the sumx firmware. I'm currently engaged with support and will update the post once a resolution has been figured out.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:57 AM . Last Modified: ‎2024-03-13 01:10 AM

0 Likes
0
2054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:57 AM . Last Modified: ‎2024-03-13 01:10 AM

I contacted support and they sent me a replacement card and all is working well now. The new card recognizes the UPS. 

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore