New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
I have 1 SMX1500RM2U and 1 SMX48RMBP2U external battery pack, with new batteries. Both are working ok, except the maximum charge rate going into the external battery pack is about 80W. At ~54 V for 4 series batteries, this amounts to about 1.5 Amps charge rate, which is way, way below the safe charge rate for these batteries. The SMX1500RM2U is able to detect the external battery pack and shows "1 external battery pack" installed. Would adding additional packs cause the SMX1500RM2U to increase it's charging rate? Or it just puts out the same amperage no matter how many external batteries are connected and adding more batteries will just cause the entire system to take longer and longer to charge?10.0.0.0.1
Last, would changing the V constant on the bhappymodattery to a slightly higher or lower setpoint cause the UPS to charge at a higher wattage?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:26 AM. Last Modified: 2024-03-1505:37 AM
Hi AmirJustin,
The maximum charger capacity of that particular unit is 103 watts, this can be seen on the units spec page (link below), the maximum will not change if more battery packs are added.
Generally UPSs will "trickle" charge, this is that they charge below their maximum, this is to increase the lifespan of the batteries and the unit (the faster a battery is charged the lower its life, roughly). It also increases power efficiency of the unit.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:26 AM. Last Modified: 2024-03-1505:37 AM
Hi AmirJustin,
The maximum charger capacity of that particular unit is 103 watts, this can be seen on the units spec page (link below), the maximum will not change if more battery packs are added.
Generally UPSs will "trickle" charge, this is that they charge below their maximum, this is to increase the lifespan of the batteries and the unit (the faster a battery is charged the lower its life, roughly). It also increases power efficiency of the unit.