SMX 3000HV max load capacity

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX 3000HV max load capacity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
8
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

SMX 3000HV max load capacity

Hi,

does anybody know what is the max load capacity of APC SMX 3000HV when main power available?

Since the load, when mains are available, does not pass through inverter the allowable load should be a bit higher, isn't it?

When on batteries, 2700W is the max load but when on mains feed whats the max load and what is the corresponding time?

Thank you.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Hi Liam,

I finalized the UPS setup with the following limits in KNX: on battery max current 11A and online 25A. Everything is working fine since then.

The client wants to repeat the setup in another house, this time though, we have a tri-phase power supply for which we intend to install 3 SMX3000HV units, one UPS for each phase. Is there any problem with this setup? One of my colleagues said that this setup is dangerous and should not be used, but I don't see why. Could you please clarify the matter?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Hi Daniel - 

When online you will get an overload tone at 2700w, but the unit will still pass power. The limiting factor is the breakers (either input or output)

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Hi Liam,

thank you for the input. So let me get this straight: if we install a 40A breaker we can pass 40A through the UPS no problem as long as we are online? That's pretty handy for my scope at least. What I intend to do is to put an entire house on UPS and then lead all 3 output groups to a KNX 8 fold switch actuator, programmed with load shedding logic, then lead the channels to 8 circuit breakers. Through a voltage sensing unit I can make 2 load shedding programs so I needed to know how far I can go with the online mode. The only thing that concerns me is that when I opened the UPS I found power relay with 20 max rated amps. Maybe the UPS, when online does not pass this load through any of these relays?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Hi Daniel - 

The UPS itself has internal fuseable links as well as breakers on the outputs. The circuit feeding it should be sized appropriately - We would recommend no more than 30amps. If you are trying to pass 40 amps through it (or close to that) you are going to run into breakers tripping. We do not advise intentionally running the unit in overload mode.

Also - you mentioned an entire house. I can't see what region you are in, but if you are in North America, please note that this unit can not support 120v loads without a stepdown transformer.

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Thank you very much for your reply Liam. I live in Romania and my max load will be closer to 30A when online. I only mentioned 40A to see how far it can go. Besides, the info might be useful for other projects too.

So again, thank you, much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Hi, Liam

I managed to implement to load shedding project I was talking about and it works quite well.

Still, during discussion with the client, some modifications are to be implemented. For that I need to know what is the overload time of the UPS when on batteries. As an example, if the house in on main feed and the instant power is 3000W and suddenly the mains are out, the UPS will switch to batteries but the load will be the same until the load shedding algorithm executes in the KNX system. The algorithm needs about 1-1.5 sec to execute. Do I have this allowance from the UPS side? Can it hold such overload for about 2 sec?

Thank you.  

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:55 PM

Hi Daniel - 

 

Overload limits for this unit are:

Alarm over 105% load

Output shutdown if over 125% load for 4 Seconds, or over 150% for 1 Second, or over 200% for 250 mSeconds

Short circuit current limit is 39A

 

We would advise that your load should not exceed 80% (2160watts)  in normal operations so that you have enough headroom for in-rush.

 

Hope this helps!

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Thank you!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

0 Likes
0
1529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:37 AM . Last Modified: ‎2024-03-07 10:54 PM

Hi Liam,

I finalized the UPS setup with the following limits in KNX: on battery max current 11A and online 25A. Everything is working fine since then.

The client wants to repeat the setup in another house, this time though, we have a tri-phase power supply for which we intend to install 3 SMX3000HV units, one UPS for each phase. Is there any problem with this setup? One of my colleagues said that this setup is dangerous and should not be used, but I don't see why. Could you please clarify the matter?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore