SMT750i don't want to go online

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT750i don't want to go online
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
dynek_apc
Crewman dynek_apc
Crewman

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
4
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

SMT750i don't want to go online

Hello All,

Few months back I bought a SMT750i and it worked just fine until today.

Today I noticed that no LED on the front were on so I started checking the menus and actually everything says 0% (Load: 0%, Batt: 0%), UPS Model is empty, etc.

If I unplug power, it makes a weird noise (don't remember it was making so much noise) but current remains available for devices plugged in.

I tried pushing the on/off button several times. I tried to push it for severals seconds (until 30sec) but nothing helps.

Any idea ?

Thank you

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

Hi,

You can reset the Smart-UPS  by

1) Turn off all attached equipment

2) Turn off the UPS

3) Unplug UPS from wall

4) Disconnect Battery

5) You may hear an audible "click" from the UPS.

6) Reconnect battery, Plug UPS in, turn UPS on


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

What options to see you available in the Control menu on the front panel LCD?

Referring to this picture, all four LEDs are still off? The ones right below the power button? And when they are all off, your attached equipment still receives power?

2276_9A34F5BF04E80C8F8525761700678F53_MMAE_7V3Q7V_f_h_500x500.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

dynek_apc
Crewman dynek_apc
Crewman

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

Hello and thank you for your answer,

All LEDs are off, see picture I took. My equipment still receive power and if I simulate a power outage, I can hear the battery take over and it starts beeping as usual when power drops.

Anything special you want me to check in the menus ?

For instance if i try to run a Self Test, it says "Only in online".

Is there a way to force a complete shutdown / reboot ?

Thank you

2274_IMG_5437.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
0
1847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

Hi,

You can reset the Smart-UPS  by

1) Turn off all attached equipment

2) Turn off the UPS

3) Unplug UPS from wall

4) Disconnect Battery

5) You may hear an audible "click" from the UPS.

6) Reconnect battery, Plug UPS in, turn UPS on


Reply

Link copied. Please paste this link to share this article on your social media post.

dynek_apc
Crewman dynek_apc
Crewman

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
0
1846
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

Fantastic! It took a while cause it's kinda stuck in a rack but I was able to take it out unplug the rear thing that makes battery go live and it came back to normal state!

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore