Hi everyone,
I'm looking to control (if possible) my SMT3000RM2U via the serial cable in terms of turning it on after a power failure and then when the utility power returns, to turn it off.
I found this post by Angela: http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/9407/turn-on-surt8000xl-remot...
which details pins 7,8 & 9 as being for this purpose, but the serial port on my SMT3000RM2U is RJ48 so I would like to know how to translate the above 7-8-9 connection to RJ48 connector.
Also- Angela mentions that the connection as a momentary (240ms) connection. What would the UPS do if the connection was constant in one state or the other (like a relay would create)?
Greatly appreciate your time!
Chuck
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:54 AM . Last Modified: 2024-03-18 03:02 AM
Hi Lilla
The cable required is actually a smart signalling cable APC part no. 940-0625A rather than a generic serial cable.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:54 AM . Last Modified: 2024-03-18 03:02 AM
Hi Charles -
Next generation Smart-UPS (anything with an LCD screen) use a different communications protocol and cable pin-out than legacy products. You can get all the details in this application note: http://www.apc.com/salestools/MPAO-9E5RB5/MPAO-9E5RB5_R1_EN.pdf
Hope that helps,
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:54 AM . Last Modified: 2024-03-18 03:02 AM
Liam- Thank you! Exactly what I was looking for. Good day!
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:54 AM . Last Modified: 2024-03-18 03:02 AM
Hi...in my case after replacing the batteries, the unit works fine, except for one thing. Whenever I plug in a Serial Data Cable into the back of the unit, and THEN plug it into a Serial Port, the UPS shuts down, or it simply will not start. With just the cable plugged into the UPS, and the other end unplugged, it runs or starts fine. I even tried a Serial to USB Adapter, and the same thing happens. I just bought a generic Serial Cable, and not this one, since it appears to be just a generic cable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:54 AM . Last Modified: 2024-03-18 03:02 AM
Hi Lilla
The cable required is actually a smart signalling cable APC part no. 940-0625A rather than a generic serial cable.
Regards