Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
SMT3000MI2U failed firmware update and recovery
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2412:50 AM
SMT3000MI2U failed firmware update and recovery
Good morning from the UK first post here.
after much looking on the forum I couldn't find this information so thought I would post to help.
I have tried to do a firmware update through AP9630 and it seemed to hang for hours.
now ups LCD does not work seems bricked.
I have tried connecting the ups via serial cable to USB (AP9827) and nothing is detected when I connect the ups vis USB a to b cable I get 2 devices appear in device manager "HID-compliant vendor-defined device" and "USB Input Device" still the firmware upgrade wizard fails to find anything.
I managed to use the NMC Firmware Update Utility to upgrade the network card to the latest version but it can't communicate with the ups.
Fix
I'm not sure how maybe someone could explain the network card picked up that the ups had a UPS has no valid firmware (this was after leaving the ups on all night)
I now have the ability to upload a firmware, I did this and now I have a working ups again