SMT2200RM2U w/ AP9630 firmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT2200RM2U w/ AP9630 firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
12
5595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

SMT2200RM2U w/ AP9630 firmware

Can anyone send me the direct link to the latest firmware download for SMT2200RM2U w/ AP9630. I tried multiple downloads from the APC software download to no avail using apc firmware upgrade utility v2.20. After  guessing what firmware is correct, I've flashed it twice with the wrong versions and I login to AP9630 it tells ne NO UPS found. Any help would ne great. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

Yep, 587 worked. Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

Hi, you can try this link and press "download now"

https://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFSUMX664&software_id=MFOI-B5NN2Y&famil... 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

Thanks for the info. What do I need to extract and install. It doesn't look like I can use apc firmware upgrade utility v2.20? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

Hi Mark

The link Angela provided is a self extracting installer for the NMC firmware.

To update the UPS firmware you can use the newer firmware wizard in this link

https://www.apc.com/uk/en/faqs/index?page=content&id=FA281865&actp=search&viewlocale=en_US&searchid=...

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

As Matt shared, if you want to upgrade the AP9630 itself, you use the file I shared with you. Instructions on applying that and how to use it are here: http://www.apc.com/us/en/faqs/FA156047

If the latest firmware is applied, which you can verify in the AP9630 under About->Network menu (should read 'aos' 6.6.4 and 'sumx' (Smart-UPS) application module 6.6.4), then you may have a different problem where correct firmware is applied for your UPS type but AP9630 still can't "see" or "talk to" the SMT UPS. 

Once you confirm the firmware I shared is applied, let us know if there is still a problem. A screenshot of the About->Network section would be helpful too from the AP9630 if you're not sure what you're seeing or what firmware is loaded.

Lastly, as Matt also shared, if there is confusion here and you're trying to upgrade the UPS device itself (separate from AP9630 Network Management Card), then you can use the FAQ he shared to do that. The AP9630 and UPS use separate firmware images and separate tools to update them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

Matt,

Thanks for the link.

Looks like this wizard is for serial firmware update. I not sure which serial cable to use with my AP9630.  I can see on the back of the AP9640 it has a mini headphone port to serial.

APC doesn't have a network firmware update tool for the AP9630? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:28 AM . Last Modified: ‎2024-03-17 11:16 PM

Hi Mark - please refer to my previous post after Matt's. You need the file I originally provided to you and you can apply it over the network (FTP) or use the .bin files contained within it for other methods (serial/XMODEM, Secure Copy- SCP).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

Thanks for your patience. I think I get it now. The AP9630 has it's own firmware and firmware update utility. I guess I did get the AP9630 updated correctly, as my first post asked. Attached is a screen shot of the "about-Network". Please verify. Second attachment is the AP9630 "home" screen, where is states "No UPS Found". 

I'm assuming that I don't have the latest firmware on the SMT2200RM2U because the AP9630 does not see the UPS. Is that correct?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Hi Mark,

No problem. Thanks for the screenshots as these were helpful in diagnosing the issue. What I am seeing is that you have 'sy' firmware module loaded which is for Symmetra model UPSs and you have a Smart-UPS product. We need to re-upgrade the firmware using the file I shared to you. 

The UPS should not need to be upgraded to establish communication with the AP9630 so you can manage it through there. But, just like for the AP9630, the UPS team provides periodic UPS firmware updates for their products with new features, enhancements, bug fixes, etc. You can choose to upgrade it if you wanted. You can see the UPS firmware under About->UPS menu (share a screenshot if you need me to check the rev and if it is out of date). As the UPS often requires a full power down of the outlets to apply its upgrade (depending on the model) and is more of a pain to do over USB or serial, you may just choose to just leave this alone until you have a reason to upgrade. An UPS upgrade is NOT usually required unless you are experiencing a specific issue or would like to take advantage of a new feature they provide.

Long story short, let's upgrade AP9630 a second time to apply the right application file for Smart-UPS products and it should fix the issue here.

Please use the file I sent at this link (https://www.apc.com/us/en/tools/download/download.cfm?sw_sku=SFSUMX664&software_id=MFOI-B5NN2Y&famil...) which the file name you need to make sure you download and apply (in case you download what I am sharing to a folder with other APC firmware files) is apc_hw05_aos664_sumx664_bootmon108.exe and it will extract three files: apc_hw05_aos_664.bin, apc_hw05_sumx_664.bin and apc_hw05_bootmon_108.bin. (Note, if you choose a manual method to upgrade, you really just need to make sure you apply the AOS file, then the sumx file.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

I think I'm good now. I sent attachment of Home screen

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

I was originally trying to setup email notification on my AP9630 and was having no luck. My email test kept failing on "Test e-mail failed; SMTP configuration error", so I decided to upgrade the firmware to see if that fix my issue. Which it did not fix. Still getting the same error. I've tried port 25 and 465.

I know my network is connecting to smtp.gmail.com. A DNS test comes back. See pic. Plus I have a NAS that is setup with the same SMTP setup and it works.

I've attached pics of my setup.

Thanks

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Hi Mark,

I successfully use Gmail with port 587 and then the other settings you have there - smtp.gmail.com, my email as the "From" address. I do believe also I've had to configure "Allow less secure apps" in the security options of my Gmail account (when not using 2 factor authentication).

If your Gmail account uses 2-factor authentication, then you won't have "Allow less secure apps" option in your account settings and you rather have to use "app passwords" option in Gmail's security settings. You basically use a specific password and your email address as the login for this specific device to use 2 factor authentication through this type of client.

I just re-tried on 6.6.4 to be sure it worked right this second and it did.

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
5589
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Angela,

Yep, 587 worked. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore