SMT2200R2X106 Battery Replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT2200R2X106 Battery Replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

0 Likes
3
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

SMT2200R2X106 Battery Replacement

We have three SMT2200R2X106 UPS devices powering our core switching and domain controllers. They have been running for nearly three years now and we're looking into replacing the batteries. Can we replace them without powering down? If so is there a resource explaining the process? Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

The RBC43 is one of the easiest battery cages to replace.  Remove the bezel, remove the three mounting screws, disconnect the blue Anderson, slide it out, slide the new one in, reconnect the blue Anderson and screws and then your done.  You should reconfigure the SMT so that it knows new batteries have been installed.  If the old battery packs have lost run-time, you might have to recalibrate the new batteries.  Just be careful - if you have the units fully loaded,  the battery can be depleted very quickly and shutdown the unit if you don't get the mains back in quickly toward the end of calibration.  A ~ 30% load is best.

These battery cages can also be "rebuilt" with new batteries quite easily.  They use 8 - 12 volt, 5 (or 5.5) AH batteries available at places like Battery Shark -  fairly inexpensively.  It does take some knowledge of batteries, polarity, and DC wiring, so don't do if you don't have such skills.

Good luck

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

Yes, the batteries can be replaced without powering down. You'll want to have the replacement batteries ready for immediate installation, as the load will not be protected against a power failure until the batteries are reinstalled.

Gently pull outward on the front bezel to remove it. At that point you should see the battery door.

The user's manual for your UPS will have complete details (some of mine might be a bit fuzzy, I'm going from memory). Unfortunately, it seems that the "manuals and documentation" link leads to a 404 not found message. Hopefully someone at APC might be able to fix that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

0 Likes
0
1132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

put her in bypass mode

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

0 Likes
0
1133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:36 AM . Last Modified: ‎2024-03-18 04:31 AM

The RBC43 is one of the easiest battery cages to replace.  Remove the bezel, remove the three mounting screws, disconnect the blue Anderson, slide it out, slide the new one in, reconnect the blue Anderson and screws and then your done.  You should reconfigure the SMT so that it knows new batteries have been installed.  If the old battery packs have lost run-time, you might have to recalibrate the new batteries.  Just be careful - if you have the units fully loaded,  the battery can be depleted very quickly and shutdown the unit if you don't get the mains back in quickly toward the end of calibration.  A ~ 30% load is best.

These battery cages can also be "rebuilt" with new batteries quite easily.  They use 8 - 12 volt, 5 (or 5.5) AH batteries available at places like Battery Shark -  fairly inexpensively.  It does take some knowledge of batteries, polarity, and DC wiring, so don't do if you don't have such skills.

Good luck

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.