SMT2200 Lower Outlets Turn off During tests

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT2200 Lower Outlets Turn off During tests
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
2
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

SMT2200 Lower Outlets Turn off During tests

Hello,

On the back of my SMT2200, whenever a test runs or the unit goes on battery, the lower outlets turn off. The unit doesn't have any special markings that indicate one set or other outlets are not battery-backed which makes me think something is setup wrong, perhaps in the Outlet configurations?

The upper row is fine. Anything plugged into runs on battery until power is restored or the battery consumes its charge.

The UPS does not have a network module. Instead, we use USB to the server hardware which runs Windows Server 2012. On there, we have the various PowerChute Business software services installed and can adjust and manage things from there.

Unfortunately, I'm remote (COVID), so any work on-site can happen but slowly. So if I need to get more information I will.

 

YYW18SbUnFbL9WRaF3F9lA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngYYW18SbUnFbL9WRaF3F9lA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Thanks all!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • power
  • PowerChute
  • shutdown
  • smart-ups
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

On 6/15/2020 11:16 AM, Bill said:

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

I'm wondering if the problem is actually a bad battery. Well, I say "bad," but it's more accurate to say "old." The unit was installed in 2013 and we've never changed the battery. Is it possible that there is a battery problem and the web page and the unit itself doesn't see it?

Thanks for your response!!

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

On 6/15/2020 11:16 AM, Bill said:

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

I'm wondering if the problem is actually a bad battery. Well, I say "bad," but it's more accurate to say "old." The unit was installed in 2013 and we've never changed the battery. Is it possible that there is a battery problem and the web page and the unit itself doesn't see it?

Thanks for your response!!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of