SMT2200 Lower Outlets Turn off During tests

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT2200 Lower Outlets Turn off During tests
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
2
1627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

SMT2200 Lower Outlets Turn off During tests

Hello,

On the back of my SMT2200, whenever a test runs or the unit goes on battery, the lower outlets turn off. The unit doesn't have any special markings that indicate one set or other outlets are not battery-backed which makes me think something is setup wrong, perhaps in the Outlet configurations?

The upper row is fine. Anything plugged into runs on battery until power is restored or the battery consumes its charge.

The UPS does not have a network module. Instead, we use USB to the server hardware which runs Windows Server 2012. On there, we have the various PowerChute Business software services installed and can adjust and manage things from there.

Unfortunately, I'm remote (COVID), so any work on-site can happen but slowly. So if I need to get more information I will.

 

YYW18SbUnFbL9WRaF3F9lA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngYYW18SbUnFbL9WRaF3F9lA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Thanks all!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • power
  • PowerChute
  • shutdown
  • smart-ups
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

On 6/15/2020 11:16 AM, Bill said:

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

I'm wondering if the problem is actually a bad battery. Well, I say "bad," but it's more accurate to say "old." The unit was installed in 2013 and we've never changed the battery. Is it possible that there is a battery problem and the web page and the unit itself doesn't see it?

Thanks for your response!!

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

0 Likes
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:19 AM . Last Modified: ‎2024-03-15 05:42 AM

On 6/15/2020 11:16 AM, Bill said:

Hi,

That is strange. A SMT2200 has 2 outlet groups. A main and a switched. The switched is Group1. The main cannot be powered off until the switch has been powered down. Open the PowerChute interface and go to Shutdown - Outlet Control. From there you can power on and power off the outlet groups remotely. You will see that the unswitched cannot be powered off until the switched has been powered off i.e. the drop down menu will be grayed out. 

LfRpfXPPQ2zO9c5wdFEJzw%3D%3D.pngLfRpfXPPQ2zO9c5wdFEJzw%3D%3D.png

I'm wondering if the problem is actually a bad battery. Well, I say "bad," but it's more accurate to say "old." The unit was installed in 2013 and we've never changed the battery. Is it possible that there is a battery problem and the web page and the unit itself doesn't see it?

Thanks for your response!!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.