Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
SMT 750 connected to Lenovo server/Win2022 loses connection out of the blue after weeks of operation and no change.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-1208:25 AM
SMT 750 connected to Lenovo server/Win2022 loses connection out of the blue after weeks of operation and no change.
On two different setups with one 750 connected to a machine running ParaChute Client the client suddenly out of the blue - after weeks of successful operation - reports communication lost. We have tried to disconnect and reconnect, reinstall Powerchute and restart machine to no avail. If I connect the UPS via USB to a PC it says 'device not recognized' if I connect same PC to another working 750 it says "APC Smartups... connected". I have not tried to restart UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-1410:50 AM. Last Modified: 2025-08-1410:54 AM
Long term fix relating to this specific problem is to use the supplied RJ50 -> RS-232 Serial cable that came with the unit to the server.
Interim break fix is to disable all power management relating to Power Chute Software.
NOTE: It has been reported disabling (Green Mode) may also help prevent this issue. Historically, doing so hasn’t fixed this problem but give it a try!