UPS: Bypass not in range ; either frequency or voltage.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: Bypass not in range ; either frequency or voltage.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
127
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

0 Likes
7
21870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

UPS: Bypass not in range ; either frequency or voltage.

We experienced a power outage where the UPS did not engage. The error in the log states "UPS: Bypass not in range ; either frequency or voltage." Based on the information below can you tell me what was the cause of this and perhaps are the settings not configured properly?

There is also quite a few "UPS Bypass not in range ; distorted wavform" events. Are these related?

Thanks

cScpi0C5rQAes%2F5uZjO55w%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngcScpi0C5rQAes%2F5uZjO55w%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Power Settings:

DSZgtuPNDvmZVnajcPXv%2Fw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngDSZgtuPNDvmZVnajcPXv%2Fw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Data log during the outage. 

Bed%2BvJjsQRaLj2oxaXuxRg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngBed%2BvJjsQRaLj2oxaXuxRg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Labels
  • Labels:
  • Getting Started
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

0 Likes
1
21857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

Hi Amine

Those messages are just making you aware that the input power to the UPS is bad quality and not good enough quality for the UPS to switch to bypass should it be required due to a UPS issue.

 

Regards

 

Matt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

0 Likes
0
21857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

Hi,

I have the same problem, no one finds the solution?

GPmSFUYhyk1J2zlExzSmvg%3D%3D.pngGPmSFUYhyk1J2zlExzSmvg%3D%3D.png

Thanks

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

0 Likes
1
21858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 11:06 PM . Last Modified: โ€Ž2024-03-19 03:22 AM

Hi Amine

Those messages are just making you aware that the input power to the UPS is bad quality and not good enough quality for the UPS to switch to bypass should it be required due to a UPS issue.

 

Regards

 

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

fabur
fabur
Cadet

Posted: โ€Ž2023-03-23 06:55 AM . Last Modified: โ€Ž2023-03-23 07:01 AM

In response to BillP
0 Likes
0
14445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-03-23 06:55 AM . Last Modified: โ€Ž2023-03-23 07:01 AM

So no way to fix this without intervention to the input power line ? 

 

I could see in Power Settings ->  Output Frequency Range  could be set to +/- 3.0 but I think it's not the right setting since we are talking about the input frequency right?


Thanks in advance. F. 

  • Tags:
  • frequency
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

RussT-1
RussT-1
Cadet

Posted: โ€Ž2023-10-20 07:45 AM

0 Likes
0
10902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-10-20 07:45 AM

How do I go about clearing  the critical alarm ?  I have no control of the input power 

Reply

Link copied. Please paste this link to share this article on your social media post.

GregF
GregF
Cadet

Posted: โ€Ž2025-07-17 12:02 PM

0 Likes
1
504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-17 12:02 PM

Hi,

  I just installed a new Smart-UPS SRT 1500 UPS and have the bypass not in range; either frequency or voltage.  Every log looks in tolerance.  How do you clear the critical alarm?  Thanks

GregF_0-1752778861182.png

GregF_1-1752778908607.png

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: โ€Ž2025-07-18 02:28 AM

In response to GregF
0 Likes
0
502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-07-18 02:28 AM

Based on the brief data log you have provided your site has unstable line input voltage.


Default the system to its factory settings and power cycle the system than compare the (Output / Bypass) upper / lower transfer voltage - once done compare to your image capture.

 

Brain Dead: Complete a brain Dead as outlined in this APC FAQ for the SRT at the bottom: 

 

https://www.apc.com/us/en/faqs/FA156611/

 

NOTE: All of the steps taken up above brings the system to an OEM Default State. It does not solve any problems you may have at this site with respect to dirty power if present. As such the system is operating as expected to protect the connected load from power quality issues.

 

You can skip all the above steps and change both settings to the widest range and report back the results to see if the fault clears.

 

The system will still need to be power cycled once the values have been updated!

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

dakotawallender
Crewman dakotawallender
Crewman

Posted: โ€Ž2025-08-14 05:30 PM

0 Likes
0
36
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-14 05:30 PM

I just want to add to this in regards to the original post's question. When we are showing bypass not in range but not on battery when there is a power input problem its because the UPS is a double conversion UPS and it can take in pretty bad power and still use it to create clean properly regulated power. ive seen 240v symmetra units have only 130 volts in and continue to work normally without going on battery. if it needs to use the battery it will.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of