SMT 1500
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:20 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
On 5/30/2018 2:23 AM, Michele said:What is the "overload protector" button on the back?
It is a circuit breaker. It works the same as a circuit breaker in a home. If there is an overload situation or a short the circuit breaker will open to protect the UPS from damage.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:19 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
If you want to send e-mail from PowerChute Business Edition to smtp.gmail.com you will first need to upgrade PowerChute to version 9.5. See Schneider Electric FAQ FA249593
The port for smtp.gmail.com is 465 Use SSL
We do not offer a test button at this time. It will be added as a feature in a future release. For now to test e-mail you can configure the software to send e-mail when a self-test is run. The through PowerChute trigger a self-test. To trigger a self-test go to Smart-UPS 750 - Diagnostics
You will find information on e-mails sent in the pcbe.log file. The default path to the log for Windows is C:\Program Files (x86)\APC\PowerChute Business Edition\agent\log
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:19 AM . Last Modified: 2024-03-17 11:58 PM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:19 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
The log show an issue resolving the SMTP host
2018-05-12 12:21:12,464 [SMTPMailWorker] WARN - [SMTPMailer.SMTPMailWorker] SMTPMailConfigException :javax.mail.MessagingException: Unknown SMTP host: smtp.gmail.com;
nested exception is:
java.net.UnknownHostException: smtp.gmail.com
2018-05-12 12:21:12,464 [SMTPMailWorker] WARN - [SMTPMailer.SMTPMailWorker] com.apcc.m11.components.SMTPMailer.SMTPMailConfigException: javax.mail.MessagingException: Unknown SMTP host: smtp.gmail.com;
nested exception is:
java.net.UnknownHostException: smtp.gmail.com
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:19 AM . Last Modified: 2024-03-17 11:58 PM
does your message mean that it is correctly configured to send emails right?
email has arrived .... but only when I unplugged the usb cable
_________________________
Let's move on to the second question
We must understand perfectly the logics of shutdown of the APC, because we will install them on industrial servers.
We need the APC to shut down the server it is connected to (Windows Server 2016) 3 minutes before it runs out.
Do you confirm the screenshot?
Another thing ... is it possible to test the auto switch-off procedure?
Thank you
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:19 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
I The screenshot show that the OS needs 3 minutes to power down. I recommend increasing the runtime limit to 5 minutes to allow a 2 minute buffer. Also you should add a minimum battery return requirement. The requirement should be determined by the amount of time the system needs to boot and to power down.
9XxlLwrxxz2eWu2SppZnGw%3D%3D.png
In the above example I add a 7 minute delay. I based this on the system needing 2 minutes to boot, 3 minutes to power down and added a 2 minute buffer. The reasoning to allow the system to safely boot up and power down in the event there is a power outage prior to the UPS fully charging.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:20 AM . Last Modified: 2024-03-17 11:58 PM
the setting for restarting the server is fundamental
now we have stopped the other purchases and we are buying only APC
APC Back-UPS BX does not have this feature true?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:20 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
The screenshots show that PowerChute will start the shutdown process when the UPS has 5 minute remaining of runtime. The UPS will what 3 minutes and then cut power to the outlets. When AC is restored the UPS will remain off until there is 7 minutes of available runtime and then the outlets will power up.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:20 AM . Last Modified: 2024-03-17 11:58 PM
ok perfect...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:20 AM . Last Modified: 2024-03-17 11:58 PM
Hi,
On 5/30/2018 2:23 AM, Michele said:What is the "overload protector" button on the back?
It is a circuit breaker. It works the same as a circuit breaker in a home. If there is an overload situation or a short the circuit breaker will open to protect the UPS from damage.