SMC1500 "Connect Battery" alarm - what does it mean?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMC1500 "Connect Battery" alarm - what does it mean?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:18 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
4
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:18 AM . Last Modified: ‎2024-03-17 11:22 PM

SMC1500 "Connect Battery" alarm - what does it mean?

My SMC began throwing this alarm.  It sits very quietly on a shelf, undisturbed, doing its job, and the battery is of course connected.  I note that there are a number of potential alarms for battery degradation and failure, but when I search this error, I see a lot of suggestions about replacing the battery.  Is this alarm typical of a bad battery?  If so, what are the other more specific battery failure alarms for?  And if this alarm indicates some other problem, how do I know?  I don't want to buy a new battery if the alarm really means "your charging circuit is bad" or "your logic board was bad".  I don't want to waste time or money.  So how can I troubleshoot this problem effectively?

Thanks,

J.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

I discovered while perusing the menus that this is an SMT, not an SMC.  Anyway, yes, it does appear one of the batteries has swelled and is making removal very difficult.  But I have no intention of throwing this expensive device in the trash because of a battery.  The device should be designed so that batteries which fail in this way are easily removable, and it should contain temperature sensors which stop the charging circuit on overheating.

J.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:18 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:18 AM . Last Modified: ‎2024-03-17 11:22 PM

Hi J,

You can initiate a self-test from the UPS display to diagnose the battery health. However, in certain cases even degraded batteries are capable of charging up to float voltage and passing the self-test. You may need management software to initiate this self-test (PoweChute Business Edition) as the SMC models don't have a Control menu on their LCD display and would otherwise self test every two weeks or whenever they are turned on.

How old is your SMC? A typical VRLA UPS battery will last between 3 to 5 years, depending on number and depth of discharges, operating temperature, etc.

Another way of troubleshooting a potentially degraded battery is to connect a (non-critical) load with known power rating to the UPS and disconnect the UPS AC input. This chart will help compare the actual UPS run time at that specific load level to the run time expected form a new battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

Thank you for the detailed reply.

I suspect it's the batteries.  It's over 4 years old and when I pull off the front cover, the battery cases are very hot and there are salts condensed on the top surface at the seams.  

I'm going to just roll the dice and get a new battery for it.

I have another question - how do you get the batteries out?  I can't quite get a grip on them and they don't seem to want to move.  I don't want to shut down the UPS or take it out of its location - that would be a chore and require me to power down the loads.

Thanks,

J.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

Hi J - 

You should immediately turn the UPS off and disconnect it from input power. When batteries get too hot or are left charging after they have failed, they can experience a state called "thermal runaway" which can cause them to swell, vent, and sometimes even leak. When a battery is in this state it is importantly to not continue charging it. Once your unit cools, you may find that the batteries are able to be removed from the unit. If they are still firmly lodged at that point you would likely need to replace the UPS. We do not recommend disassembling the case to remove a swollen battery due to potential safety hazards. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:19 AM . Last Modified: ‎2024-03-17 11:22 PM

I discovered while perusing the menus that this is an SMT, not an SMC.  Anyway, yes, it does appear one of the batteries has swelled and is making removal very difficult.  But I have no intention of throwing this expensive device in the trash because of a battery.  The device should be designed so that batteries which fail in this way are easily removable, and it should contain temperature sensors which stop the charging circuit on overheating.

J.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore