SMC1000C
Hi
I have an issue with My APC Smart UPS (SMT1000C). I have no power on output, I was check with the Volt meter and output said 0 Volts. But the screen of SMT said 120V on Output?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:35 AM. Last Modified: 2024-03-1504:56 AM
Hi,
If the Smart-UPS is an SMT1000C you should verify the outlet groups are on. If the outlet groups are off no AC would be present. You can check the output via the LCD panel under status.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:35 AM. Last Modified: 2024-03-1504:56 AM
Hi,
If the Smart-UPS is an SMT1000C you should verify the outlet groups are on. If the outlet groups are off no AC would be present. You can check the output via the LCD panel under status.