SMART UPS RT 3000 VA crashed total after power outage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART UPS RT 3000 VA crashed total after power outage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:24 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
10
1872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:24 AM . Last Modified: ‎2024-03-11 02:38 AM

SMART UPS RT 3000 VA crashed total after power outage

Hi,
in a customer situation a SMART UPS RT 3000VA with SNMP Card crashed totally
after a power outage.

The power outage occured exactly during the time when I was with PCNS logged into
my Windows XP Client and I was checking the log entries of the UPS.

After power comes up again the UPS don't turns on any more. Also the FAN is not running.
Every three seconds a beep comes out. Thats all.

This UPS system runs some years without errors and I tested in this time 50 times
power outage. The UPS switched on battery and switched back after power restore
without errors. Battery is good. Every 14 days automatic testing.

2 hours before that happens I tested again a power outage and power
restoring and all is OK.

The Software I use is Power Chute Network Shutdown PCNS and its working
very fine.

Does anyone have an idea what do to? I can't image that the UPS has an defect.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

I have a SMART-UPS RT 3000 and it happened a error and some transistors are burned and i can not see the numbers that are named the transistors.how can you help me

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

can you get the log files from any of the powerchute network shutdown clients or the network management card? this would help a great deal.

instructions on getting network management card logs are here: http://nam-en.apc.com/app/answers/detail/a_id/9321

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

Hi,
thanks for reply.
Of course I think about this, but:
- The SNMP-Card is NOT under voltage, no blinking of the LEDs
- Also I can't get contact via the RS232C connection with 2400 Baud.
I can't switch on the UPS anymore.
Do the UPS have a kind of main fuse on the motherboard which are broken?
I think the bug is at the beginning of the power.
Do you have an idea?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

First you should replace the UPS batteries ( Having 12 V each) because issue is in UPS not in NMC Card.
UPS can switch on without NMC Card So remove the NMC then check if ups is working or not?

Regards,
Aftab

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

Hi,

thanks for your Idea.I have i too.
I replace the SNMP Card but the UPS is not working.

But I have the solution now.
The Beep Code every 4 Seconds mean the UPS can't get contact with the Battery
or in other words the UPS can not start because the Batteries are defect.

I take my measuring instrument and without Input Power I see 206V from
both Batteries together. OK, this is fine I thought.
But: Plugging in the Power the voltage shows 92V. So the Batteries are defect
and have to be replaced by new ones. Ths UPS need a voltage of 170 V to start.

It is very interessting for me to see that the Battery Test I did every 2 weeks don't
show an error.
But I have learned that I have to do once or twice a year a Loadtest with the UPS.
This is better as looking into the log and see the Battery Test is working.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

hi,
sory for late reply,
In SURT Series minimum Voltage required for Each Battery is 86 VDC.So please verifiy while using multimeter what are the each Battery Module Voltages ?
I think each Battery Module Voltages are less then 86 Volts so thats why UPS is not Switching on.
So if UPS d,nt Switch on so it will not possible to Shitf on Bypass Mode.

2nd thing if you d,nt want to purchase new Battery Modules for your UPS then if you have another SURT Series UPS then you can utilize its batteries for Switching on the Faulty UPS.

Regards,
Aftab Ghauri























google music, pandora, limewire

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

Some news to this old UPS of type SURT3000XLI.

I remember that of course this UPS has a Manual Bypass Switch at the back.

And so I pull both batteries out and switch to Manual Bypass.
Then switching Input Power on but nothing happens!

So now it has nothing to do with a battery anymore. I don't want to buy two
new batteries, putting these into the UPS and the UPS is NOT starting.

So I think now the UPS has an defect. But I'm disappointed beccause this
very expensive UPS refused to obey with the MAIN FUNCTION, don't cut off
the Output Power if the Input Power fails.

Some points to think about:
- There was no "please replace the Battery" Alarm with LED ON at the Front Panel
- All 2 weeks the Battery check returns OK
- Manual Bypass Switch is not working; LED is not ON.
- One day before breakdown of this UPS I removed the Input Power for 5 minutes and all was OK

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

Hi Aftab Ghauri,

well, thank you. This is very interested.

I forgot the following and I will repeat your ideas:
- I can only switch from Online to Bypass with the switch at the back IF THE UPS IS ON.
- This is now OK and I understand.
- In other words: The UPS has to start before.
- This is an ONLINE UPS and we need the voltage level you wrote in the post (86 volt per Battery)
- This is also OK
- Input Power is not connected at this time.
- I measure for one Battery a voltage of 103 Volts or 206 Volts for both but THIS IS NOT UNDER LOAD.
- I measure for both Batteries a voltage of 92 Volts during pressing the ON Switch. This is under load.
- That means one Battery has a voltage of 46V under load and this is too less for starting the UPS.
- If you agree with my sentences both Batteries are defekt (for your: both batteries have an age of 6.5 years..........)

Regards, Hans

Message was edited by: Magnussen

Message was edited by: Magnussen

Message was edited by: Magnussen

Message was edited by: Magnussen

Message was edited by: Magnussen

Message was edited by: Magnussen

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

Hi Magnussen,
your are 100 % right and now you had findout the Solution of your faulty UPS.

Regards,
Aftab Ghauri






















red tube, pandora, limewire

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

I have a SMART-UPS RT 3000 and it happened a error and some transistors are burned and i can not see the numbers that are named the transistors.how can you help me

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

0 Likes
0
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:25 AM . Last Modified: ‎2024-03-11 02:38 AM

one clarification on SURT3000 - the bypass is a logical/electronic bypass - it is not really a manual or mechanical bypass in my mind because its not a physical switch that moves with or without good DC voltage on other UPS types.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of