Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2903:04 AM. Last Modified: 2024-03-1303:18 AM
SMART UPS Broke
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2903:04 AM. Last Modified: 2024-03-1303:18 AM
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2903:04 AM. Last Modified: 2024-03-1303:18 AM
Hi,
Due to a terrible mistake, I had connected 230 V on a OUT connector of my Smart Ups 1500 VA.
The UPS not go on, practically is dead.
How can I repair it?
Thank you