SMART UPS 3000 problem
Hello
Here is my problem with UPS. I have model SUA3000RMI2U with batteries replaced in Jun 2014. While trying to run a self-test, it failed:UPS: At least one faulty battery exists.
UPS alarm test is passed
I removed the batteries, checked UPS output voltage (55.08VDC) as well as mechanical connection and all looks fine. And since batteries are relatively new, I am not sure if they are problem or the problem is with the UPS itself. When running self test, the bad battery red LED is ON
I have another model of this UPS and it passes self-test. I have also redundancy switch installed.
What should I do next? Replace batteries again? Please advise.
Slawomir.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Hi Slawomir,
Since you have another model of the UPS, I would swap that battery temporarily into this UPS and run a manual self test. This way you tell whether the issue is with the battery or the UPS.
Other thoughts:
- Did you purchase a genuine APC battery or purchase third party ones? If it's a genuine APC battery, there should be a white sticker with a model and serial number on it which will be helpful determining the age of the battery.
- Do you have frequent power outages or an unusual environment (ie. overly hot, etc.)?
- How long did the batteries last before you swapped them in June 2014? (knowing the UPS serial number would be helpful as well)
- Does this failed self test message occur when the UPS runs it automatically or when you run it manually?
Let me know what you find out.
- Tommy
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:30 AM . Last Modified: 2024-03-18 11:13 PM
Link copied. Please paste this link to share this article on your social media post.