ACSC100 Supplemental HVAC Requirements/Considerations per APC App Note #109

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ACSC100 Supplemental HVAC Requirements/Considerations per APC App Note #109
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

0 Likes
2
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

ACSC100 Supplemental HVAC Requirements/Considerations per APC App Note #109

In case anyone out there was not already aware of it, the ACSC100 standalone cooler does require some supplementary HVAC in order for it to continue to operate.

For each ACSC unit, there must be 850cfm minimum airflow in the plenum above the ceiling (i.e.: it must be an "active" plenum). Also, the air in this plenum that reaches the inlet of the ACSC cannot exceed 105 degF (40 degC). Typically, this temperature should be cooler than that so that the unit does not shut down due to high head pressure. Bringing air in from outside for this purpose will not be applicable in all regions, in part, due to the requirement that the air be over 32 degF.

Typically, the building system will be utilized to provide this air. However, even if the active plenum above the standalone cooling unit happens to be a return air plenum, keep in mind that during the cooling season, an additional BTU load will be placed on the building comfort cooling system.

As a sidenote, when the building comfort HVAC is used to remove/cool this air, it is interesting to note that the end user will be paying to cool this air twice. Once when it is moved from their data center to the active plenum, and once more as it is cooled by the air handler for comfort cooling.

It also is important to understand the impact that this will have on the building cooling system in order to ensure that there will be enough capacity to accomodate the additional cooling load while still maintaining setpoint. This will be more significant when there are multiple ASCS standalone units installed.

We currently have two of these units installed at our location and they are working great. In terms of dropping in cooling where there is no chilled water and where options are limited as to piping out to external condensers, this is a really terrific solution and it uses very little floor space.

However, I am mentioning this because it is not at all obvious from APC's specifications on the unit itself (on the APC website) that any additional HVAC engineering must be taken into consideration when installing these units.

It took me some time to reach the right people in the APC cooling product division who were able to share this information.

There is also an application note #92 "Best Practices for Designing Data Centers
with the InfraStruXure InRow RC" that is a very valuable resource when determining where to place these units, etc. I tried to attach this document, but it was too large for the discussion forum's attachment size limit. Sadly, I do not have the URL to reach it.

At the time of my posting this, the information from APC application note #109 (as well as any link to the application note itself) still does not appear on the ASCS100 product web page:
https://www.apcc.com/resource/include/techspec_index.cfm?base_sku=ACSC100&tab=documentation

So, I am posting this info here as a reference to anyone who is planning on installing the unit so that they can have a successful experience right out of the gate by being aware of the unit's HVAC requirements in advance.

- John

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

0 Likes
0
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

In case anyone out there was not already aware of it, the ACSC100 standalone cooler does require some supplementary HVAC in order for it to continue to operate.

For each ACSC unit, there must be 850cfm minimum airflow in the plenum above the ceiling (i.e.: it must be an "active" plenum). Also, the air in this plenum that reaches the inlet of the ACSC cannot exceed 105 degF (40 degC). Typically, this temperature should be cooler than that so that the unit does not shut down due to high head pressure. Bringing air in from outside for this purpose will not be applicable in all regions, in part, due to the requirement that the air be over 32 degF.

Typically, the building system will be utilized to provide this air. However, even if the active plenum above the standalone cooling unit happens to be a return air plenum, keep in mind that during the cooling season, an additional BTU load will be placed on the building comfort cooling system.

As a sidenote, when the building comfort HVAC is used to remove/cool this air, it is interesting to note that the end user will be paying to cool this air twice. Once when it is moved from their data center to the active plenum, and once more as it is cooled by the air handler for comfort cooling.

It also is important to understand the impact that this will have on the building cooling system in order to ensure that there will be enough capacity to accomodate the additional cooling load while still maintaining setpoint. This will be more significant when there are multiple ASCS standalone units installed.

We currently have two of these units installed at our location and they are working great. In terms of dropping in cooling where there is no chilled water and where options are limited as to piping out to external condensers, this is a really terrific solution and it uses very little floor space.

However, I am mentioning this because it is not at all obvious from APC's specifications on the unit itself (on the APC website) that any additional HVAC engineering must be taken into consideration when installing these units.

It took me some time to reach the right people in the APC cooling product division who were able to share this information.

There is also an application note #92 "Best Practices for Designing Data Centers
with the InfraStruXure InRow RC" that is a very valuable resource when determining where to place these units, etc. I tried to attach this document, but it was too large for the discussion forum's attachment size limit. Sadly, I do not have the URL to reach it.

At the time of my posting this, the information from APC application note #109 (as well as any link to the application note itself) still does not appear on the ASCS100 product web page:
https://www.apcc.com/resource/include/techspec_index.cfm?base_sku=ACSC100&tab=documentation

So, I am posting this info here as a reference to anyone who is planning on installing the unit so that they can have a successful experience right out of the gate by being aware of the unit's HVAC requirements in advance.

- John

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

0 Likes
0
837
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

Thank you for the additional information. There is no question that you made the future implementation of the ACSC100 better for me, I'm better prepared now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

0 Likes
0
838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:30 AM . Last Modified: ‎2024-03-18 11:13 PM

In case anyone out there was not already aware of it, the ACSC100 standalone cooler does require some supplementary HVAC in order for it to continue to operate.

For each ACSC unit, there must be 850cfm minimum airflow in the plenum above the ceiling (i.e.: it must be an "active" plenum). Also, the air in this plenum that reaches the inlet of the ACSC cannot exceed 105 degF (40 degC). Typically, this temperature should be cooler than that so that the unit does not shut down due to high head pressure. Bringing air in from outside for this purpose will not be applicable in all regions, in part, due to the requirement that the air be over 32 degF.

Typically, the building system will be utilized to provide this air. However, even if the active plenum above the standalone cooling unit happens to be a return air plenum, keep in mind that during the cooling season, an additional BTU load will be placed on the building comfort cooling system.

As a sidenote, when the building comfort HVAC is used to remove/cool this air, it is interesting to note that the end user will be paying to cool this air twice. Once when it is moved from their data center to the active plenum, and once more as it is cooled by the air handler for comfort cooling.

It also is important to understand the impact that this will have on the building cooling system in order to ensure that there will be enough capacity to accomodate the additional cooling load while still maintaining setpoint. This will be more significant when there are multiple ASCS standalone units installed.

We currently have two of these units installed at our location and they are working great. In terms of dropping in cooling where there is no chilled water and where options are limited as to piping out to external condensers, this is a really terrific solution and it uses very little floor space.

However, I am mentioning this because it is not at all obvious from APC's specifications on the unit itself (on the APC website) that any additional HVAC engineering must be taken into consideration when installing these units.

It took me some time to reach the right people in the APC cooling product division who were able to share this information.

There is also an application note #92 "Best Practices for Designing Data Centers
with the InfraStruXure InRow RC" that is a very valuable resource when determining where to place these units, etc. I tried to attach this document, but it was too large for the discussion forum's attachment size limit. Sadly, I do not have the URL to reach it.

At the time of my posting this, the information from APC application note #109 (as well as any link to the application note itself) still does not appear on the ASCS100 product web page:
https://www.apcc.com/resource/include/techspec_index.cfm?base_sku=ACSC100&tab=documentation

So, I am posting this info here as a reference to anyone who is planning on installing the unit so that they can have a successful experience right out of the gate by being aware of the unit's HVAC requirements in advance.

- John

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of