SMART UPS 1000I NET - too old or still OK?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART UPS 1000I NET - too old or still OK?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
8
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

SMART UPS 1000I NET - too old or still OK?

Hello everybody!

I have a question regarding my old UPS.
I am going to put some pictures of the unit and a print-screen from the info menu in the powerchute. According to those info's, if there are accurate, this unit was manufactured in 1997... that's quite some time... almoust 14 years, seems preety much, if you ask me. I purchased the UPS, refurbished, in 2005.
The unit is performing very well, but God knows what's inside.

My question is if it's still safe to use it ? What is the life expectancy of those units? Or, if it was "refurbished" so it means that all the "almoust dead" components like capacitors, transistors, etc... were replaced in service?

What are you people saying about this? I would like also an APC tehnician or employee to answer this.


Thank you very much!
Adrian.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 1000i
  • emergency
  • explosion
  • fault
  • fire
  • insurance
  • liability
  • meltdown
  • overload
  • PowerChute
  • smart-ups
  • su2200
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 03:10 AM . Last Modified: β€Ž2024-03-08 04:53 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:10 AM . Last Modified: β€Ž2024-03-08 04:53 AM

Hi

I have two older ups, over 10 years, both serial, and both have had their batteries replaced.

When I found out the Apple Macs would not support them, I bought two keyspan serial - usb converters
and used apcupsd to local/remote monitor them.

I since have purchased a smaller apc ups for my usb based NAS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

ahahaha πŸ˜„

You are very right, if it's about a server room where everything it's modern, black, etc... indeed, it doesn't look nice at all.
But mine is at my home, in my loft πŸ™‚ So, the aesthetic part doesn't matter. I was asking only if it's safe or not to use it anymore, because yeah, it's really old and don't want to have a fire or something in the loft of my house πŸ˜›

Cheers!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

hi adrian,

do you know WHERE it was refurbished? our supported service partner is Coastal Business Machines.

Most APC UPSs have a life expectancy of 10 years. as long as you keep replacing the battery if it fails, since it is consumable, then you should be good to go. i don't know what exactly was refurbished on your particular unit to be honest with you but the electronics inside could fail from age i would assume, unless they were actually replaced. also, the UPS has surge protection. over the years, it may have taken some surges and over time, the surge protection could degrade from accepting surges.

but, if it is still working, i would use it. we have a lifetime equipment protection policy on these units if any attached equipment fails and it is found to be the cause of the UPS. if you take care of it, it should work fine. i cannot speak though for your particular unit and the condition of the electronics inside since I did not see it, but i don't think its a bad idea to continue to use the UPS. just take care of that battery and ensure the unit continues to work properly and transfers to battery, etc

Reply

Link copied. Please paste this link to share this article on your social media post.

Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

As far as I know, all APC UPS's going back a decade or more will contain extensive power filtering and fault handling capabilities, so if the unit were to develop a problem such as a welded power relay, a blown surge-suppression MOV, or a leaking/blown power capacitor, at most it will just "stop working" rather than exploding in a fireball and taking your chateau with it.

The APC UPS electronics are also inside a very heavy and almost fully-enclosing steel case so even if it did overload and melt down internally, I highly doubt the damage would spread beyond a singed floor, unless you have your UPS under your table saw sitting in a bed of wood shavings and sawdust, next to your ammunition reloading supplies...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

Hello!

No, I don't know where it was refurbished, but I will try to ask the company from where I purchased the unit.
If so, I am still going to use the unit, because as far as I see... APC is really "legendary reliable " :))

If I will have more informations, I'll let you know πŸ™‚

Thank you!
Adrian.

Reply

Link copied. Please paste this link to share this article on your social media post.

Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

The main difference between newer and older units is the power conversion efficiency. In older UPS's it is around 75%, newer ones are around 90%. This means you either:

- run longer / have more VA capacity with same battery capacity as older model
- run same amount of time / same VA capacity as older with smaller batteries

Oh and the old ones are beige. That is SO unstylish and retro. They are also squarer with less styling of the plastic.

How can you even tolerate that in a server room? πŸ˜‰

Message was edited by: Javik

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

Hi ADI


I have two UPS units, a 1000I and a 2200, I have installed the single node business edition of powerchute, and tried connecting to my 1000I( the 2200 batteries are not sorted yet) however I dont get a screen anything like yours, mine is in a web browser and offers very little info and will only communicate via simple comms and not smart, how did you get the screen shot you posted?

Im running win 7 with usb - serial converter if it makes a difference.

Thanks Herishi

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

0 Likes
0
2238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:09 AM . Last Modified: β€Ž2024-03-08 04:54 AM

Hello Herishi,

The screen capture that ADI has posted is the GUI of our PowerChute Business Edition Console. Also, if you have a Smart-UPS unit the best connection would be Smart-Signaling in order for you to see all the details that our unit can provide. What is connected to the UPS? Is it the serial cable? If it is make sure it is either the 940-0024 or 940-1524. If you are using a Serial to USB adapter, it would also be helpful if you could verify from the manufacturer if it requires a software driver.

Also, when you install PCBE make sure that you choose the Auto-Detect UPS features first.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 03:10 AM . Last Modified: β€Ž2024-03-08 04:53 AM

0 Likes
0
2239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 03:10 AM . Last Modified: β€Ž2024-03-08 04:53 AM

Hi

I have two older ups, over 10 years, both serial, and both have had their batteries replaced.

When I found out the Apple Macs would not support them, I bought two keyspan serial - usb converters
and used apcupsd to local/remote monitor them.

I since have purchased a smaller apc ups for my usb based NAS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of