Multiple Smart-UPS RT 6000 XL configuration in Powerchute problem
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3003:09 AM. Last Modified: 2024-03-0804:54 AM
Multiple Smart-UPS RT 6000 XL configuration in Powerchute problem
Hi All,
Here is a bit about our setup first:
We have 2x Smart-UPS RT 6000 XL units with network management cards
We are running Powerchute from a network server
Powerchute is connected to the management cards of both UPSs
UPSs are set to do a graceful shutdown via Powerchute when the battery duration is under 20 minutes
We also have a command file that runs with Powerchute
Although our setup is redundant we do not have an equal load on each server due to APC switches for single power devices
The problem is that as we do not have an equal load on each server the batteries drain at different rates. This means that the UPSs both get to the specified low battery duration at completely different times. The problem here is that UPS 1 may have run down to 5 minutes and is in deperate need of intiating a Powerchute shutdown - UPS 2 still has 25 minutes of runtime so no shutdown is initiated. Consequently UPS 1 goes down and takes all the servers with and then shuts down UPS 2 as well! What we need to happen are 1 of either 2 things:
1. Powerchute initiates the shutdown as soon as either UPS reaches the 20 minutes low battery duration setting - and doesnt wait for both
or
2. The UPS with the heavier load expends its entire battery but does not shutdown both UPSs and lets the load be switched across to the UPS that still has runtime remaining. That way when the UPS that still has runtime reaches its low battery duration it can proceed with the graceful shutdown via Powerchute.
Hope that makes sense, any help is greatly appreciated!