SL20KHB2 silicon. error message "STOP CHARGE DC CAPACITOR YES"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SL20KHB2 silicon. error message "STOP CHARGE DC CAPACITOR YES"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
3
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

SL20KHB2 silicon. error message "STOP CHARGE DC CAPACITOR YES"

Hi all
Am a ups engineer but not familiar with slicon model.
Unit model : SL20KHB2 silicon

PROBLEM: according the engineer on site
In the morning the unit was found down
The unit was found with both DC batteries fuse brown, both the fuses were replaced but still the unit could not power up
The case was report to us and site visit has been carried

DIAGNOSIS CARRED:

(A) Found blown fuse in the in put RFI PCB , and replaced the fuse blown fuse
(B) Open the entire unit checking for physical damage /bad component ,all fuses ,tested inverter IGBT & several PBCs, none found bad
(c) Tested the battery module voltage, per module the lowest reading was = 99V , high = 102V
(d) After connected back the mains and unit power up but indicating Aram message: ‘’Stop charge DC capacitor- YES’’
(d) Unit powered ,No active button on the control panel and no output

This error ”STOP CHARGE DC CAPACITOR- YES” is not mentioned in the alarm massage in the service manual
kindly advise me.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

Hi
Thanks for the help, but my customer decided to buy a new unit VT-30KVA, said the unit old. Before exercising those instruction.
I really missed to see it work

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

Hi,

1. You fuse is blown down may be due to get deep discharged with very high current.

Please help follow this instruction:

0. Open the door , you will see the push button red/ green. in the large metal steel.

1. Turn off the UPS, turn off the Battery Breaker Box, keep the fuse still on.
(if you battery is internal type, please get out the battery DC fuse.)

2. Check again the DC capacitor if there are any fault.

3. Turn on CB supply the power to input UPS.

4. You will see the messege "’Stop charge DC capacitor- YES’’

press the Battery icon in the keypad and see how much the voltage charge . It' will increase slow up to 435V DC.

press "#" to confirm storp charge the DC. (if the DC low, you must press "C", "#" to start again"

5. insert fuse /or turn on the MCCB.

6. press green button 1 time.

7. The UPS will start.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

You should call into your local APC service office for support. Silcon UPS are too complex to troubleshoot on a web forum.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

Hi
Thanks for the help, but my customer decided to buy a new unit VT-30KVA, said the unit old. Before exercising those instruction.
I really missed to see it work

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore